[I] [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress

yangshuyi opened a new issue, #1450:
URL: https://github.com/apache/plc4x/issues/1450

   ### What would you like to happen?
   
   When I try to connect Modbus and read data from address with a slave id like 22, I cannot find the slave id configuration in the plc4j-driver-modbus library. 
   
   I get a little confused, because other's lib like modbus4j has this feature.
   
   
   Without slave id, it looks always reading from a default slave-id, like 1 which does not exist, then it will cause timeout exception:
   
   java.util.concurrent.ExecutionException: java.util.concurrent.TimeoutException
           at java.base/java.util.concurrent.CompletableFuture.reportGet(CompletableFuture.java:396)
           at java.base/java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2073)
           at com.primustech.siriusplus.dae.modbus.client.ModbusReader.readData(ModbusReader.java:82)
           at com.primustech.siriusplus.dae.modbus.processor.ModbusConnPoolingThread.readData(ModbusConnPoolingThread.java:20)
           at com.primustech.siriusplus.dae.core.processor.ConnPollingThreadAbstract.lambda$run$0(ConnPollingThreadAbstract.java:43)
           at com.primustech.siriusboot.common.base.tracelog.utils.TracelogSpringScheduleUtils.execute(TracelogSpringScheduleUtils.java:20)
           at com.primustech.siriusplus.dae.core.processor.ConnPollingThreadAbstract.run(ConnPollingThreadAbstract.java:42)
           at java.base/java.lang.VirtualThread.run(VirtualThread.java:309)
   Caused by: java.util.concurrent.TimeoutException: null
           at org.apache.plc4x.java.spi.netty.NettyHashTimerTimeoutManager.lambda$0(NettyHashTimerTimeoutManager.java:54)
           at io.netty.util.HashedWheelTimer$HashedWheelTimeout.run(HashedWheelTimer.java:715)
           at io.netty.util.concurrent.ImmediateExecutor.execute(ImmediateExecutor.java:34)
           at io.netty.util.HashedWheelTimer$HashedWheelTimeout.expire(HashedWheelTimer.java:703)
           at io.netty.util.HashedWheelTimer$HashedWheelBucket.expireTimeouts(HashedWheelTimer.java:790)
           at io.netty.util.HashedWheelTimer$Worker.run(HashedWheelTimer.java:503)
           at java.base/java.lang.Thread.run(Thread.java:1583)
   
   ### Programming Languages
   
   - [X] plc4j
   - [ ] plc4go
   - [ ] plc4c
   - [ ] plc4net
   
   ### Protocols
   
   - [ ] AB-Ethernet
   - [ ] ADS /AMS
   - [ ] BACnet/IP
   - [ ] CANopen
   - [ ] DeltaV
   - [ ] DF1
   - [ ] EtherNet/IP
   - [ ] Firmata
   - [ ] KNXnet/IP
   - [X] Modbus
   - [ ] OPC-UA
   - [ ] S7


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org.apache.org

For queries about this service, please contact Infrastructure at:
users@infra.apache.org


Re: [I] [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress

Posted by "yangshuyi (via GitHub)" <gi...@apache.org>.
yangshuyi closed issue #1450: [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress
URL: https://github.com/apache/plc4x/issues/1450


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org

For queries about this service, please contact Infrastructure at:
users@infra.apache.org


Re: [I] [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress

Posted by "splatch (via GitHub)" <gi...@apache.org>.
splatch commented on issue #1450:
URL: https://github.com/apache/plc4x/issues/1450#issuecomment-2003631810

   If its about various slave ids then its a duplicate of #1234.


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org

For queries about this service, please contact Infrastructure at:
users@infra.apache.org


Re: [I] [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress

Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #1450:
URL: https://github.com/apache/plc4x/issues/1450#issuecomment-2011634520

   I added the comment "or slave-id" to the description of the unit-identifier.


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org

For queries about this service, please contact Infrastructure at:
users@infra.apache.org


Re: [I] [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress

Posted by "yangshuyi (via GitHub)" <gi...@apache.org>.
yangshuyi commented on issue #1450:
URL: https://github.com/apache/plc4x/issues/1450#issuecomment-2010999350

   Got it. I tried and it works. It might be good if the document can update. Thanks a lot.


-- 
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.

To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org

For queries about this service, please contact Infrastructure at:
users@infra.apache.org


Re: [I] [Feature Request]: plc4j-driver-modbus need to have Slave Id configuration when reading TagAddress

Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #1450:
URL: https://github.com/apache/plc4x/issues/1450#issuecomment-1993883527

   The "unit-identifier" doesn't help? https://plc4x.apache.org/users/protocols/modbus.html It's part of the connection-string.


-- 