"Discarded Message"... How do I start debugging this?

Hi All,

I'm trying to make my first steps, but already hitting a roadblock: My
minimal code seems stuck on getConnection, and I've no idea how to debug
this.

I'm really trying to do something minimal, inspired by the example code,
and reading the first 4 input pins of my S7-200. I see the "START" log
entry, but not the "CONNECTED" one, meaning I never complete the connection
step. The only suspicious thing I see is this:

Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0,
IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0,
DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x5148d82b, L:/
192.168.1.16:53396 - R:/192.168.1.222:102]."

Full disclosure: I'm using an off-brand adapter because I can't afford a
proper Siemens CP 243-1. Can that cause the issue?
How do I even begin to debug this?

Thanks,
  Fred

----- my code -----
static final String connectionString = "s7://192.168.1.222/0/2";

public static void main(String[] args) {
    logger.info("----- START -----");
    try (PlcConnection plcConnection = new
PlcDriverManager().getConnection(connectionString)) {
        logger.info("----- CONNECTED -----");
        if (!plcConnection.getMetadata().canRead()) {
            logger.error("This connection doesn't support reading.");
            return;
        }
        PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
        builder.addItem("value-1", "%I0.0:BOOL");
        builder.addItem("value-2", "%I0.1:BOOL");
        builder.addItem("value-3", "%I0.2:BOOL");
        builder.addItem("value-4", "%I0.3:BOOL");
        PlcReadRequest readRequest = builder.build();
        logger.info(readRequest.execute().get().toString());
        logger.info("----- DONE -----");
    } catch (Exception e) {
        e.printStackTrace();
    }

----- the output -----
INFO  S7Test - ----- START -----
INFO  o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver
Manager with class loader sun.misc.Launcher$AppClassLoader@18b4aac2
INFO  o.apache.plc4x.java.PlcDriverManager - Registering available
drivers...
INFO  o.apache.plc4x.java.PlcDriverManager - Registering driver for
Protocol s7 (Siemens S7 (Basic))
DEBUG i.n.u.i.l.InternalLoggerFactory - Using SLF4J as the default logging
framework
DEBUG io.netty.util.ResourceLeakDetector - -Dio.netty.leakDetection.level:
simple
[...lots of Netty debug output removed here...]
DEBUG io.netty.util.Recycler - -Dio.netty.recycler.ratio: 8
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
11d00001000200c2020200c1020102c0010a
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 queued
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 sent
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@480c8d80 that
reached at the tail of the pipeline. Please check your pipeline
configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
[S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
02f080320300000000000800000000f0010001000100f0
INFO  o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established
pdu-size 240, max-amq-caller 1, max-amq-callee 1
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 queued
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 received
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 sent
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@64b0dea4 that
reached at the tail of the pipeline. Please check your pipeline
configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
[S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].

Re: "Discarded Message"... How do I start debugging this?

Posted by Frédéric Auberson <fr...@gmail.com>.
Chris, you're amazing! This did the trick:

INFO  S7Test - ----- CONNECTED -----
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 received
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@648ba43b that reached at the tail of the pipeline. Please check your pipeline configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x15572297, L:/192.168.1.16:62767 - R:/192.168.1.222:102].
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 1 queued
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 1 sent
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data: 02f0803203000000010002001700000404ff0300010100ff0300010000ff0300010000ff03000101
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 1 received
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@47553a05 that reached at the tail of the pipeline. Please check your pipeline configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x15572297, L:/192.168.1.16:62767 - R:/192.168.1.222:102].
INFO  S7Test - Value[value-1]: true
INFO  S7Test - Value[value-2]: false
INFO  S7Test - Value[value-3]: false
INFO  S7Test - Value[value-4]: true
INFO  S7Test - ----- DONE -----
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.p.j.s.connection.S7PlcConnection - Remote didn't close connection within the configured timeout of 1000 ms, shutting down actively.
java.util.concurrent.TimeoutException: null
	at java.util.concurrent.CompletableFuture.timedGet(CompletableFuture.java:1771)
	at java.util.concurrent.CompletableFuture.get(CompletableFuture.java:1915)
	at org.apache.plc4x.java.s7.connection.S7PlcConnection.close(S7PlcConnection.java:253)
	at S7Test.main(S7Test.java:62)
DEBUG io.netty.buffer.PoolThreadCache - Freed 3 thread-local buffer(s) from thread: nioEventLoopGroup-2-1


My connection String was s7://192.168.1.222/0/2?controller-type=S7_300, it worked like a charm...

On 12.11.19, 14:57, "Christofer Dutz" <ch...@c-ware.de> wrote:

    Hi Frederic,
    
    While thinking about what could be going wrong I had the following idea:
    When connecting to an S7 as soon as the IsoTP and the S7 login is finished, the driver asks the S7 to identify itself.
    I would assume something is going wrong here ... so if you are unable to provide a WireShark dump, you can skip the identification step, if you tell the driver which S7 type you are expecting.
    
    So could you please give this connection string a try?
    
    s7://{ip}/{rack}/{slot}?controller-type=S7_300
    
    For if, rack and slot just use your normal values ... the important part is to add the "?controller-type=S7_300" to the end of your existing connection string.
    
    I know you have a S7-200 ... but we don't have a constant for the 200 as the 200 generally doesn't support this protocol.
    
    Please tell us if this works.
    
    Chris
    
    
    Am 12.11.19, 06:49 schrieb "Christofer Dutz" <ch...@c-ware.de>:
    
        Hi Frederic,
        
        First of all, a warm welcome here. I am sorry to hear that you are having trouble. If course it could be that the hardware is causing trouble. I guess the only way to find out what's going wrong would be to do a Wireshark recording of the communication.
        
        Then we can be sure what's going wrong.
        
        The discarded incoming message, is definitely the cause, but I don't know what could be causing this.
        
        Could you do a Wireshark capture, create a jira issue and attach it to that? Then I'll have a look.
        
        Chris
        ________________________________
        Von: Fr?d?ric Auberson <fr...@gmail.com>
        Gesendet: Montag, 11. November 2019 14:52:44
        An: dev@plc4x.apache.org <de...@plc4x.apache.org>
        Betreff: "Discarded Message"... How do I start debugging this?
        
        Hi All,
        
        I'm trying to make my first steps, but already hitting a roadblock: My
        minimal code seems stuck on getConnection, and I've no idea how to debug
        this.
        
        I'm really trying to do something minimal, inspired by the example code,
        and reading the first 4 input pins of my S7-200. I see the "START" log
        entry, but not the "CONNECTED" one, meaning I never complete the connection
        step. The only suspicious thing I see is this:
        
        Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0,
        IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0,
        DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x5148d82b, L:/
        192.168.1.16:53396 - R:/192.168.1.222:102]."
        
        Full disclosure: I'm using an off-brand adapter because I can't afford a
        proper Siemens CP 243-1. Can that cause the issue?
        How do I even begin to debug this?
        
        Thanks,
          Fred
        
        ----- my code -----
        static final String connectionString = "s7://192.168.1.222/0/2";
        
        public static void main(String[] args) {
            logger.info("----- START -----");
            try (PlcConnection plcConnection = new
        PlcDriverManager().getConnection(connectionString)) {
                logger.info("----- CONNECTED -----");
                if (!plcConnection.getMetadata().canRead()) {
                    logger.error("This connection doesn't support reading.");
                    return;
                }
                PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
                builder.addItem("value-1", "%I0.0:BOOL");
                builder.addItem("value-2", "%I0.1:BOOL");
                builder.addItem("value-3", "%I0.2:BOOL");
                builder.addItem("value-4", "%I0.3:BOOL");
                PlcReadRequest readRequest = builder.build();
                logger.info(readRequest.execute().get().toString());
                logger.info("----- DONE -----");
            } catch (Exception e) {
                e.printStackTrace();
            }
        
        ----- the output -----
        INFO  S7Test - ----- START -----
        INFO  o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver
        Manager with class loader sun.misc.Launcher$AppClassLoader@18b4aac2
        INFO  o.apache.plc4x.java.PlcDriverManager - Registering available
        drivers...
        INFO  o.apache.plc4x.java.PlcDriverManager - Registering driver for
        Protocol s7 (Siemens S7 (Basic))
        DEBUG i.n.u.i.l.InternalLoggerFactory - Using SLF4J as the default logging
        framework
        DEBUG io.netty.util.ResourceLeakDetector - -Dio.netty.leakDetection.level:
        simple
        [...lots of Netty debug output removed here...]
        DEBUG io.netty.util.Recycler - -Dio.netty.recycler.ratio: 8
        DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
        DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
        DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
        11d00001000200c2020200c1020102c0010a
        DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 queued
        DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
        DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 sent
        DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
        org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@480c8d80 that
        reached at the tail of the pipeline. Please check your pipeline
        configuration.
        DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
        [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
        Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
        0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
        DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
        DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
        02f080320300000000000800000000f0010001000100f0
        INFO  o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established
        pdu-size 240, max-amq-caller 1, max-amq-callee 1
        DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 queued
        DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 received
        DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
        DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 sent
        DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
        org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@64b0dea4 that
        reached at the tail of the pipeline. Please check your pipeline
        configuration.
        DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
        [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
        Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
        0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
        
    
    

Re: "Discarded Message"... How do I start debugging this?

Posted by Christofer Dutz <ch...@c-ware.de>.
Hi Frederic,

While thinking about what could be going wrong I had the following idea:
When connecting to an S7 as soon as the IsoTP and the S7 login is finished, the driver asks the S7 to identify itself.
I would assume something is going wrong here ... so if you are unable to provide a WireShark dump, you can skip the identification step, if you tell the driver which S7 type you are expecting.

So could you please give this connection string a try?

s7://{ip}/{rack}/{slot}?controller-type=S7_300

For if, rack and slot just use your normal values ... the important part is to add the "?controller-type=S7_300" to the end of your existing connection string.

I know you have a S7-200 ... but we don't have a constant for the 200 as the 200 generally doesn't support this protocol.

Please tell us if this works.

Chris


Am 12.11.19, 06:49 schrieb "Christofer Dutz" <ch...@c-ware.de>:

    Hi Frederic,
    
    First of all, a warm welcome here. I am sorry to hear that you are having trouble. If course it could be that the hardware is causing trouble. I guess the only way to find out what's going wrong would be to do a Wireshark recording of the communication.
    
    Then we can be sure what's going wrong.
    
    The discarded incoming message, is definitely the cause, but I don't know what could be causing this.
    
    Could you do a Wireshark capture, create a jira issue and attach it to that? Then I'll have a look.
    
    Chris
    ________________________________
    Von: Fr?d?ric Auberson <fr...@gmail.com>
    Gesendet: Montag, 11. November 2019 14:52:44
    An: dev@plc4x.apache.org <de...@plc4x.apache.org>
    Betreff: "Discarded Message"... How do I start debugging this?
    
    Hi All,
    
    I'm trying to make my first steps, but already hitting a roadblock: My
    minimal code seems stuck on getConnection, and I've no idea how to debug
    this.
    
    I'm really trying to do something minimal, inspired by the example code,
    and reading the first 4 input pins of my S7-200. I see the "START" log
    entry, but not the "CONNECTED" one, meaning I never complete the connection
    step. The only suspicious thing I see is this:
    
    Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0,
    IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0,
    DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x5148d82b, L:/
    192.168.1.16:53396 - R:/192.168.1.222:102]."
    
    Full disclosure: I'm using an off-brand adapter because I can't afford a
    proper Siemens CP 243-1. Can that cause the issue?
    How do I even begin to debug this?
    
    Thanks,
      Fred
    
    ----- my code -----
    static final String connectionString = "s7://192.168.1.222/0/2";
    
    public static void main(String[] args) {
        logger.info("----- START -----");
        try (PlcConnection plcConnection = new
    PlcDriverManager().getConnection(connectionString)) {
            logger.info("----- CONNECTED -----");
            if (!plcConnection.getMetadata().canRead()) {
                logger.error("This connection doesn't support reading.");
                return;
            }
            PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
            builder.addItem("value-1", "%I0.0:BOOL");
            builder.addItem("value-2", "%I0.1:BOOL");
            builder.addItem("value-3", "%I0.2:BOOL");
            builder.addItem("value-4", "%I0.3:BOOL");
            PlcReadRequest readRequest = builder.build();
            logger.info(readRequest.execute().get().toString());
            logger.info("----- DONE -----");
        } catch (Exception e) {
            e.printStackTrace();
        }
    
    ----- the output -----
    INFO  S7Test - ----- START -----
    INFO  o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver
    Manager with class loader sun.misc.Launcher$AppClassLoader@18b4aac2
    INFO  o.apache.plc4x.java.PlcDriverManager - Registering available
    drivers...
    INFO  o.apache.plc4x.java.PlcDriverManager - Registering driver for
    Protocol s7 (Siemens S7 (Basic))
    DEBUG i.n.u.i.l.InternalLoggerFactory - Using SLF4J as the default logging
    framework
    DEBUG io.netty.util.ResourceLeakDetector - -Dio.netty.leakDetection.level:
    simple
    [...lots of Netty debug output removed here...]
    DEBUG io.netty.util.Recycler - -Dio.netty.recycler.ratio: 8
    DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
    DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
    DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
    11d00001000200c2020200c1020102c0010a
    DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 queued
    DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
    DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 sent
    DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
    org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@480c8d80 that
    reached at the tail of the pipeline. Please check your pipeline
    configuration.
    DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
    [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
    Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
    0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
    DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
    DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
    02f080320300000000000800000000f0010001000100f0
    INFO  o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established
    pdu-size 240, max-amq-caller 1, max-amq-callee 1
    DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 queued
    DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 received
    DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
    DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 sent
    DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
    org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@64b0dea4 that
    reached at the tail of the pipeline. Please check your pipeline
    configuration.
    DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
    [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
    Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
    0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
    


AW: "Discarded Message"... How do I start debugging this?

Posted by Christofer Dutz <ch...@c-ware.de>.
Hi Frederic,

First of all, a warm welcome here. I am sorry to hear that you are having trouble. If course it could be that the hardware is causing trouble. I guess the only way to find out what's going wrong would be to do a Wireshark recording of the communication.

Then we can be sure what's going wrong.

The discarded incoming message, is definitely the cause, but I don't know what could be causing this.

Could you do a Wireshark capture, create a jira issue and attach it to that? Then I'll have a look.

Chris
________________________________
Von: Fr?d?ric Auberson <fr...@gmail.com>
Gesendet: Montag, 11. November 2019 14:52:44
An: dev@plc4x.apache.org <de...@plc4x.apache.org>
Betreff: "Discarded Message"... How do I start debugging this?

Hi All,

I'm trying to make my first steps, but already hitting a roadblock: My
minimal code seems stuck on getConnection, and I've no idea how to debug
this.

I'm really trying to do something minimal, inspired by the example code,
and reading the first 4 input pins of my S7-200. I see the "START" log
entry, but not the "CONNECTED" one, meaning I never complete the connection
step. The only suspicious thing I see is this:

Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0,
IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0,
DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x5148d82b, L:/
192.168.1.16:53396 - R:/192.168.1.222:102]."

Full disclosure: I'm using an off-brand adapter because I can't afford a
proper Siemens CP 243-1. Can that cause the issue?
How do I even begin to debug this?

Thanks,
  Fred

----- my code -----
static final String connectionString = "s7://192.168.1.222/0/2";

public static void main(String[] args) {
    logger.info("----- START -----");
    try (PlcConnection plcConnection = new
PlcDriverManager().getConnection(connectionString)) {
        logger.info("----- CONNECTED -----");
        if (!plcConnection.getMetadata().canRead()) {
            logger.error("This connection doesn't support reading.");
            return;
        }
        PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
        builder.addItem("value-1", "%I0.0:BOOL");
        builder.addItem("value-2", "%I0.1:BOOL");
        builder.addItem("value-3", "%I0.2:BOOL");
        builder.addItem("value-4", "%I0.3:BOOL");
        PlcReadRequest readRequest = builder.build();
        logger.info(readRequest.execute().get().toString());
        logger.info("----- DONE -----");
    } catch (Exception e) {
        e.printStackTrace();
    }

----- the output -----
INFO  S7Test - ----- START -----
INFO  o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver
Manager with class loader sun.misc.Launcher$AppClassLoader@18b4aac2
INFO  o.apache.plc4x.java.PlcDriverManager - Registering available
drivers...
INFO  o.apache.plc4x.java.PlcDriverManager - Registering driver for
Protocol s7 (Siemens S7 (Basic))
DEBUG i.n.u.i.l.InternalLoggerFactory - Using SLF4J as the default logging
framework
DEBUG io.netty.util.ResourceLeakDetector - -Dio.netty.leakDetection.level:
simple
[...lots of Netty debug output removed here...]
DEBUG io.netty.util.Recycler - -Dio.netty.recycler.ratio: 8
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
11d00001000200c2020200c1020102c0010a
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 queued
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 sent
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@480c8d80 that
reached at the tail of the pipeline. Please check your pipeline
configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
[S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
02f080320300000000000800000000f0010001000100f0
INFO  o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established
pdu-size 240, max-amq-caller 1, max-amq-callee 1
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 queued
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 received
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 sent
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@64b0dea4 that
reached at the tail of the pipeline. Please check your pipeline
configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
[S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].

Re: "Discarded Message"... How do I start debugging this?

Posted by César García <ce...@ceos.com.ve>.
Hi,


Please, try this recipe

https://support.industry.siemens.com/cs/document/19724696/¿cómo-se-configura-una-comunicación-entre-un-wincc-flexible-runtime-o-un-panel-basado-en-windows-y-un-s7-200-(cp-243-1)-a-través-de-ethernet-?dti=0&lc=es-CL

Best regards,

Enviado mediante Bandeja de entrada de BlackBerry Hub+ para Android


	  Mensaje original  



De: frederic.auberson@gmail.com
Enviados: 11 de noviembre de 2019 15:58
Para: dev@plc4x.apache.org
Responder a: dev@plc4x.apache.org
Asunto: "Discarded Message"... How do I start debugging this?


Hi All,

I'm trying to make my first steps, but already hitting a roadblock: My
minimal code seems stuck on getConnection, and I've no idea how to debug
this.

I'm really trying to do something minimal, inspired by the example code,
and reading the first 4 input pins of my S7-200. I see the "START" log
entry, but not the "CONNECTED" one, meaning I never complete the connection
step. The only suspicious thing I see is this:

Discarded message pipeline : [S7PlcConnection$1$1#0, IsoOnTcpProtocol#0,
IsoTPProtocol#0, S7Protocol#0, Plc4XS7Protocol#0,
DefaultChannelPipeline$TailContext#0]. Channel : [id: 0x5148d82b, L:/
192.168.1.16:53396 - R:/192.168.1.222:102]."

Full disclosure: I'm using an off-brand adapter because I can't afford a
proper Siemens CP 243-1. Can that cause the issue?
How do I even begin to debug this?

Thanks,
  Fred

----- my code -----
static final String connectionString = "s7://192.168.1.222/0/2";

public static void main(String[] args) {
    logger.info("----- START -----");
    try (PlcConnection plcConnection = new
PlcDriverManager().getConnection(connectionString)) {
        logger.info("----- CONNECTED -----");
        if (!plcConnection.getMetadata().canRead()) {
            logger.error("This connection doesn't support reading.");
            return;
        }
        PlcReadRequest.Builder builder = plcConnection.readRequestBuilder();
        builder.addItem("value-1", "%I0.0:BOOL");
        builder.addItem("value-2", "%I0.1:BOOL");
        builder.addItem("value-3", "%I0.2:BOOL");
        builder.addItem("value-4", "%I0.3:BOOL");
        PlcReadRequest readRequest = builder.build();
        logger.info(readRequest.execute().get().toString());
        logger.info("----- DONE -----");
    } catch (Exception e) {
        e.printStackTrace();
    }

----- the output -----
INFO  S7Test - ----- START -----
INFO  o.apache.plc4x.java.PlcDriverManager - Instantiating new PLC Driver
Manager with class loader sun.misc.Launcher$AppClassLoader@18b4aac2
INFO  o.apache.plc4x.java.PlcDriverManager - Registering available
drivers...
INFO  o.apache.plc4x.java.PlcDriverManager - Registering driver for
Protocol s7 (Siemens S7 (Basic))
DEBUG i.n.u.i.l.InternalLoggerFactory - Using SLF4J as the default logging
framework
DEBUG io.netty.util.ResourceLeakDetector - -Dio.netty.leakDetection.level:
simple
[...lots of Netty debug output removed here...]
DEBUG io.netty.util.Recycler - -Dio.netty.recycler.ratio: 8
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
11d00001000200c2020200c1020102c0010a
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 queued
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 sent
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@480c8d80 that
reached at the tail of the pipeline. Please check your pipeline
configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
[S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message received
DEBUG o.a.p.j.isotp.protocol.IsoTPProtocol - Got Data:
02f080320300000000000800000000f0010001000100f0
INFO  o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established
pdu-size 240, max-amq-caller 1, max-amq-callee 1
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 queued
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 0 received
DEBUG o.a.p.j.i.protocol.IsoOnTcpProtocol - ISO on TCP Message sent
DEBUG o.a.plc4x.java.s7.netty.S7Protocol - S7 Message with id 2 sent
DEBUG i.n.channel.DefaultChannelPipeline - Discarded inbound message
org.apache.plc4x.java.isotp.protocol.model.IsoTPMessage@64b0dea4 that
reached at the tail of the pipeline. Please check your pipeline
configuration.
DEBUG i.n.channel.DefaultChannelPipeline - Discarded message pipeline :
[S7PlcConnection$1$1#0, IsoOnTcpProtocol#0, IsoTPProtocol#0, S7Protocol#0,
Plc4XS7Protocol#0, DefaultChannelPipeline$TailContext#0]. Channel : [id:
0x5148d82b, L:/192.168.1.16:53396 - R:/192.168.1.222:102].