[GitHub] [plc4x] SteinOv commented on issue #710: modbus-tcp Write Request coil always set to false

SteinOv commented on issue #710:
URL: https://github.com/apache/plc4x/issues/710#issuecomment-1362763771

   I found the cause of the bug!
   On line 144 in the write() method in ModbusTcpProtocolLogic there is a ModbusPDU object called requestPdu. This object has a field "value" which is a byte[]. In release 0.9.1 this array contains one value: 0 if false was set and 1 if true was set. In release 0.10.0 this array contains two values. The first seems to be always 0 and the second is 0 if false was set and 1 if true was set.
   This array originates from the fromPlcValue() method. I hardcoded it to return `new byte[]{1};` and then the coils are set to true.
   
   I'll try to figure further what is going wrong exactly and how to fix it.


-- 