Posted to common-user@hadoop.apache.org by elton sky <el...@gmail.com> on 2011/06/06 09:22:58 UTC
Why inter-rack communication in mapreduce slow?
hello everyone,
As I don't have experience with big scale cluster, I cannot figure out why
the inter-rack communication in a mapreduce job is "significantly" slower
than intra-rack.
I saw cisco catalyst 4900 series switch can reach upto 320Gbps forwarding
capacity. Connected with 48 nodes with 1Gbps ethernet each, it should not be
much contention at the switch, is it?
Can anyone explain how this "slow"ness happens to me?
Thanks
Elton
Re: Why inter-rack communication in mapreduce slow?
Posted by elton sky <el...@gmail.com>.
Thanks Joey,
So the b/w is throttled by the core switch when many nodes are requesting
traffic and the core switch can not keep up.
It's only happens when the cluster is busy enough.
On Mon, Jun 6, 2011 at 11:01 PM, Joey Echeverria <jo...@cloudera.com> wrote:
> Larger Hadoop installations are space dense, 20-40 nodes per rack.
> When you get to that density with multiple racks, it becomes expensive
> to buy a switch with enough capacity for all of the nodes in all of
> the racks. The typical solution is to install a switch per rack with
> uplinks to a core switch to route between the racks. In this
> arrangement, you'll be limited by the uplink bandwidth to the core
> switch for interrack communication. Typically these uplinks are 10-20
> Gbps (bidirectional).
>
> Assuming you have 32 nodes in a rack with 1 Gbps links, then 20 Gbps
> isn't enough bandwidth to push all of those ports at full tilt between
> racks. That's why Hadoop has the ability to take advantage of rack
> locality. It will try to schedule I/O local to a rack where it's less
> likely to block.
>
> -Joey
>
> On Mon, Jun 6, 2011 at 7:04 AM, elton sky <el...@gmail.com> wrote:
> > Thanks for reply, Steve,
> >
> > I totally agree benchmark is a good idea. But the problem is I don't have
> > switch to play with rather than a small cluster.
> > I am curious of this and post the question.
> > Can some experienced ppl can share their knowledge with us?
> >
> > Cheers
> >
> > On Mon, Jun 6, 2011 at 7:28 PM, Steve Loughran <st...@apache.org>
> wrote:
> >
> >> On 06/06/11 08:22, elton sky wrote:
> >>
> >>> hello everyone,
> >>>
> >>> As I don't have experience with big scale cluster, I cannot figure out
> why
> >>> the inter-rack communication in a mapreduce job is "significantly"
> slower
> >>> than intra-rack.
> >>> I saw cisco catalyst 4900 series switch can reach upto 320Gbps
> forwarding
> >>> capacity. Connected with 48 nodes with 1Gbps ethernet each, it should
> not
> >>> be
> >>> much contention at the switch, is it?
> >>>
> >>
> >> I don't know enough about these switches; I do hear stories about
> buffering
> >> and the like, and I also hear that a lot of switches don't always expect
> all
> >> the ports to light up simultaneously.
> >>
> >> Outside hadoop, try setting up some simple bandwidth tests to measure
> >> inter-rack bandwidth: have every node on one rack try and talk to one on
> >> another at full rate.
> >>
> >> Set up every node talking to every other node at least once, to make
> sure
> >> there aren't odd problems between two nodes, which can happen if one of
> the
> >> NICs is playing up.
> >>
> >> Once you are happy that the basic bandwidth between servers is OK, then
> >> it's time to start worrying adding hadoop to the mix
> >>
> >> -steve
> >>
> >
>
>
>
> --
> Joseph Echeverria
> Cloudera, Inc.
> 443.305.9434
>
RE: Why inter-rack communication in mapreduce slow?
Posted by Michael Segel <mi...@hotmail.com>.
> Date: Tue, 7 Jun 2011 11:24:53 +1000
> Subject: Re: Why inter-rack communication in mapreduce slow?
> From: eltonsky9404@gmail.com
> To: common-user@hadoop.apache.org
>
> Michael,
> >Depending on your hardware, that's a fabric of 40GB, shared.
> So that fabric is shared by all 42 ports. And even if I just used 2 ports
> out of 42, connecting to 2 racks, if there's enough traffic coming, these 2
> ports could use all 40GB. Is this right?
>
> -Elton
>
Elton,
That 40GB is shared across all of the ports in the switch. But the maximum bandwidth each port can handle is only 1GBe bidirectional.
So if you've got 40GB/s of traffic w only 1 1GBe port, you can only push 1GB/s through the port.
I realize I'm over simplifying it, but that's the basic problem. This is why you will find switches that have 1GBe ports with 10GBe uplinks.
HTH
-Mike
> On Tue, Jun 7, 2011 at 1:42 AM, Michael Segel <mi...@hotmail.com>wrote:
>
> >
> > Well the problem is pretty basic.
> >
> > Take your typical 1 GBe switch with 42 ports.
> > Each port is capable of doing 1 GBe in each direction across the switche's
> > fabric.
> > Depending on your hardware, that's a fabric of 40GB, shared.
> >
> > Depending on your hardware, you are usually using 1 or maybe 2 ports to
> > 'trunk' to your network's back plane. (To keep this simple, lets just say
> > that its a 1-2 GBe 'trunk' to your next rack.
> > So you end up with 1GBe traffic from each node trying to communicate to
> > another node on the next rack. So if that's 20 nodes per rack and they all
> > want to communicate... you end up with 20 GBe (each direction) trying to fit
> > through a 1 - 2 GBe pipe.
> >
> > Think of Rush hour in Chicago, or worse, rush hour in Atlanta where people
> > don't know how to drive. :-P
> >
> > The quick fix... spend the 8-10K per switch to get a ToR that has 10+ GBe
> > uplink capabilities. (usually 4 ports) Then you have at least 10 GBe per
> > rack.
> >
> > JMHO
> >
> > -Mike
> >
> >
> >
> > > To: common-user@hadoop.apache.org
> > > Subject: Re: Why inter-rack communication in mapreduce slow?
> > > Date: Mon, 6 Jun 2011 11:00:05 -0400
> > > From: darren@ontrenet.com
> > >
> > >
> > > IMO, that's right. Because map/reduce/hadoop was originally designed for
> > > that kind of text processing purpose. (i.e. few stages, low dependency,
> > > highly parallel).
> > >
> > > Its when one tries to solve general purpose algorithms of modest
> > > complexity that map/reduce gets into I/O churning problems.
> > >
> > > On Mon, 6 Jun 2011 23:58:53 +1000, elton sky <el...@gmail.com>
> > > wrote:
> > > > Hi John,
> > > >
> > > > Because for map task, job tracker tries to assign them to local data
> > > nodes,
> > > > so there' not much n/w traffic.
> > > > Then the only potential issue will be, as you said, reducers, which
> > > copies
> > > > data from all maps.
> > > > So in other words, if the application only creates small intermediate
> > > > output, e.g. grep, wordcount, this jam between racks is not likely
> > > happen,
> > > > is it?
> > > >
> > > >
> > > > On Mon, Jun 6, 2011 at 11:40 PM, John Armstrong
> > > > <jo...@ccri.com>wrote:
> > > >
> > > >> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
> > > >> > Yeah, that's a good point.
> > > >> >
> > > >> > I wonder though, what the load on the tracker nodes (port et. al)
> > > would
> > > >> > be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
> > > >> >
> > > >> > Seems to me that if there is that much traffic being mitigate across
> > > >> > racks, that the tracker node (or whatever node it is) would overload
> > > >> > first?
> > > >>
> > > >> It could happen, but I don't think it would always. For example,
> > > tracker
> > > >> is on rack A; sees that the best place to put reducer R is on rack B;
> > > >> sees
> > > >> reducer still needs a few hellabytes from mapper M on rack C; tells M
> > > to
> > > >> send data to R; switches on B and C get throttled, leaving A free to
> > > >> handle
> > > >> other things.
> > > >>
> > > >> In fact, it almost makes me wonder if an ideal setup is not only to
> > > have
> > > >> each of the main control daemons on their own nodes, but to put THOSE
> > > >> nodes
> > > >> on their own rack and keep all the data elsewhere.
> > > >>
> >
> >
Re: Why inter-rack communication in mapreduce slow?
Posted by elton sky <el...@gmail.com>.
Michael,
>Depending on your hardware, that's a fabric of 40GB, shared.
So that fabric is shared by all 42 ports. And even if I just used 2 ports
out of 42, connecting to 2 racks, if there's enough traffic coming, these 2
ports could use all 40GB. Is this right?
-Elton
On Tue, Jun 7, 2011 at 1:42 AM, Michael Segel <mi...@hotmail.com>wrote:
>
> Well the problem is pretty basic.
>
> Take your typical 1 GBe switch with 42 ports.
> Each port is capable of doing 1 GBe in each direction across the switche's
> fabric.
> Depending on your hardware, that's a fabric of 40GB, shared.
>
> Depending on your hardware, you are usually using 1 or maybe 2 ports to
> 'trunk' to your network's back plane. (To keep this simple, lets just say
> that its a 1-2 GBe 'trunk' to your next rack.
> So you end up with 1GBe traffic from each node trying to communicate to
> another node on the next rack. So if that's 20 nodes per rack and they all
> want to communicate... you end up with 20 GBe (each direction) trying to fit
> through a 1 - 2 GBe pipe.
>
> Think of Rush hour in Chicago, or worse, rush hour in Atlanta where people
> don't know how to drive. :-P
>
> The quick fix... spend the 8-10K per switch to get a ToR that has 10+ GBe
> uplink capabilities. (usually 4 ports) Then you have at least 10 GBe per
> rack.
>
> JMHO
>
> -Mike
>
>
>
> > To: common-user@hadoop.apache.org
> > Subject: Re: Why inter-rack communication in mapreduce slow?
> > Date: Mon, 6 Jun 2011 11:00:05 -0400
> > From: darren@ontrenet.com
> >
> >
> > IMO, that's right. Because map/reduce/hadoop was originally designed for
> > that kind of text processing purpose. (i.e. few stages, low dependency,
> > highly parallel).
> >
> > Its when one tries to solve general purpose algorithms of modest
> > complexity that map/reduce gets into I/O churning problems.
> >
> > On Mon, 6 Jun 2011 23:58:53 +1000, elton sky <el...@gmail.com>
> > wrote:
> > > Hi John,
> > >
> > > Because for map task, job tracker tries to assign them to local data
> > nodes,
> > > so there' not much n/w traffic.
> > > Then the only potential issue will be, as you said, reducers, which
> > copies
> > > data from all maps.
> > > So in other words, if the application only creates small intermediate
> > > output, e.g. grep, wordcount, this jam between racks is not likely
> > happen,
> > > is it?
> > >
> > >
> > > On Mon, Jun 6, 2011 at 11:40 PM, John Armstrong
> > > <jo...@ccri.com>wrote:
> > >
> > >> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
> > >> > Yeah, that's a good point.
> > >> >
> > >> > I wonder though, what the load on the tracker nodes (port et. al)
> > would
> > >> > be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
> > >> >
> > >> > Seems to me that if there is that much traffic being mitigate across
> > >> > racks, that the tracker node (or whatever node it is) would overload
> > >> > first?
> > >>
> > >> It could happen, but I don't think it would always. For example,
> > tracker
> > >> is on rack A; sees that the best place to put reducer R is on rack B;
> > >> sees
> > >> reducer still needs a few hellabytes from mapper M on rack C; tells M
> > to
> > >> send data to R; switches on B and C get throttled, leaving A free to
> > >> handle
> > >> other things.
> > >>
> > >> In fact, it almost makes me wonder if an ideal setup is not only to
> > have
> > >> each of the main control daemons on their own nodes, but to put THOSE
> > >> nodes
> > >> on their own rack and keep all the data elsewhere.
> > >>
>
>
RE: Why inter-rack communication in mapreduce slow?
Posted by Michael Segel <mi...@hotmail.com>.
Chris,
I've gone back through the thread and here's Elton's initial question...
> >> On 06/06/11 08:22, elton sky wrote:
> >>
> >>> hello everyone,
> >>>
> >>> As I don't have experience with big scale cluster, I cannot figure out
> why
> >>> the inter-rack communication in a mapreduce job is "significantly"
> slower
> >>> than intra-rack.
> >>> I saw cisco catalyst 4900 series switch can reach upto 320Gbps
> forwarding
> >>> capacity. Connected with 48 nodes with 1Gbps ethernet each, it should
> not
> >>> be
> >>> much contention at the switch, is it?
> >>>
Elton's question deals with why connections within the same switch are faster than connections that traverse a set of switches.
The issue isn't so much one of the fabric within the switch itself, but the width of the connection between the two switches.
If you have 40GBs (each direction) on a switch and you want it to communicate seamlessly with machines on the next switch, you have to have be able to bond 4 10GBe ports together.
(Note: there's a bit more to it, but its the general idea.)
You're going to have a significant slow down on communication between nodes that are on different racks because of the bandwidth limitations on the ports used to connect the switches and not the 'fabric' within the switch itself.
To your point, you can monitor your jobs and see how much of your work is being done by 'data local' tasks. In one job we had 519 tasks started where 482 were 'data local'.
So we had ~93% of the jobs where we didn't have an issue with any network latency. And then with the 7% of the jobs, you have to consider what percentage would have occurred where the data traffic is going to involve pulling data across a 'trunk'. So yes, network latency isn't going to be a huge factor in terms of improving overall efficiency.
However, that's just for Hadoop. What happens when you run HBase? ;-)
(You can have more network traffic during a m/r job.)
HTH
-Mike
Re: Why inter-rack communication in mapreduce slow?
Posted by Chris Smith <cs...@gmail.com>.
Elton,
Rapleaf's blog has an interesting posting on their experience that's
worth a read: http://blog.rapleaf.com/dev/2010/08/26/analyzing-some-interesting-networks-for-mapreduce-clusters/
And if you want to get an idea of the interaction between CPU, Disk
and Network there nothing like a picture, see Slide 9 in this deck, of
a very simply Terasort Map/Reduce job. Obviously the real world is
very different but the individual Map/Reduce jobs follow a similar
pattern.
Even doubling the node network performance in this simple example
would not get you much performance improvement as the job is CPU bound
for 50% of the time and only uses the network for roughly 10% of the
remaining time.
Chris
On 6 June 2011 16:42, Michael Segel <mi...@hotmail.com> wrote:
>
> Well the problem is pretty basic.
>
> Take your typical 1 GBe switch with 42 ports.
> Each port is capable of doing 1 GBe in each direction across the switche's fabric.
> Depending on your hardware, that's a fabric of 40GB, shared.
>
> Depending on your hardware, you are usually using 1 or maybe 2 ports to 'trunk' to your network's back plane. (To keep this simple, lets just say that its a 1-2 GBe 'trunk' to your next rack.
> So you end up with 1GBe traffic from each node trying to communicate to another node on the next rack. So if that's 20 nodes per rack and they all want to communicate... you end up with 20 GBe (each direction) trying to fit through a 1 - 2 GBe pipe.
>
> Think of Rush hour in Chicago, or worse, rush hour in Atlanta where people don't know how to drive. :-P
>
> The quick fix... spend the 8-10K per switch to get a ToR that has 10+ GBe uplink capabilities. (usually 4 ports) Then you have at least 10 GBe per rack.
>
> JMHO
>
> -Mike
>
>
>
>> To: common-user@hadoop.apache.org
>> Subject: Re: Why inter-rack communication in mapreduce slow?
>> Date: Mon, 6 Jun 2011 11:00:05 -0400
>> From: darren@ontrenet.com
>>
>>
>> IMO, that's right. Because map/reduce/hadoop was originally designed for
>> that kind of text processing purpose. (i.e. few stages, low dependency,
>> highly parallel).
>>
>> Its when one tries to solve general purpose algorithms of modest
>> complexity that map/reduce gets into I/O churning problems.
>>
>> On Mon, 6 Jun 2011 23:58:53 +1000, elton sky <el...@gmail.com>
>> wrote:
>> > Hi John,
>> >
>> > Because for map task, job tracker tries to assign them to local data
>> nodes,
>> > so there' not much n/w traffic.
>> > Then the only potential issue will be, as you said, reducers, which
>> copies
>> > data from all maps.
>> > So in other words, if the application only creates small intermediate
>> > output, e.g. grep, wordcount, this jam between racks is not likely
>> happen,
>> > is it?
>> >
>> >
>> > On Mon, Jun 6, 2011 at 11:40 PM, John Armstrong
>> > <jo...@ccri.com>wrote:
>> >
>> >> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
>> >> > Yeah, that's a good point.
>> >> >
>> >> > I wonder though, what the load on the tracker nodes (port et. al)
>> would
>> >> > be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>> >> >
>> >> > Seems to me that if there is that much traffic being mitigate across
>> >> > racks, that the tracker node (or whatever node it is) would overload
>> >> > first?
>> >>
>> >> It could happen, but I don't think it would always. For example,
>> tracker
>> >> is on rack A; sees that the best place to put reducer R is on rack B;
>> >> sees
>> >> reducer still needs a few hellabytes from mapper M on rack C; tells M
>> to
>> >> send data to R; switches on B and C get throttled, leaving A free to
>> >> handle
>> >> other things.
>> >>
>> >> In fact, it almost makes me wonder if an ideal setup is not only to
>> have
>> >> each of the main control daemons on their own nodes, but to put THOSE
>> >> nodes
>> >> on their own rack and keep all the data elsewhere.
>> >>
>
RE: Why inter-rack communication in mapreduce slow?
Posted by Michael Segel <mi...@hotmail.com>.
Well the problem is pretty basic.
Take your typical 1 GBe switch with 42 ports.
Each port is capable of doing 1 GBe in each direction across the switche's fabric.
Depending on your hardware, that's a fabric of 40GB, shared.
Depending on your hardware, you are usually using 1 or maybe 2 ports to 'trunk' to your network's back plane. (To keep this simple, lets just say that its a 1-2 GBe 'trunk' to your next rack.
So you end up with 1GBe traffic from each node trying to communicate to another node on the next rack. So if that's 20 nodes per rack and they all want to communicate... you end up with 20 GBe (each direction) trying to fit through a 1 - 2 GBe pipe.
Think of Rush hour in Chicago, or worse, rush hour in Atlanta where people don't know how to drive. :-P
The quick fix... spend the 8-10K per switch to get a ToR that has 10+ GBe uplink capabilities. (usually 4 ports) Then you have at least 10 GBe per rack.
JMHO
-Mike
> To: common-user@hadoop.apache.org
> Subject: Re: Why inter-rack communication in mapreduce slow?
> Date: Mon, 6 Jun 2011 11:00:05 -0400
> From: darren@ontrenet.com
>
>
> IMO, that's right. Because map/reduce/hadoop was originally designed for
> that kind of text processing purpose. (i.e. few stages, low dependency,
> highly parallel).
>
> Its when one tries to solve general purpose algorithms of modest
> complexity that map/reduce gets into I/O churning problems.
>
> On Mon, 6 Jun 2011 23:58:53 +1000, elton sky <el...@gmail.com>
> wrote:
> > Hi John,
> >
> > Because for map task, job tracker tries to assign them to local data
> nodes,
> > so there' not much n/w traffic.
> > Then the only potential issue will be, as you said, reducers, which
> copies
> > data from all maps.
> > So in other words, if the application only creates small intermediate
> > output, e.g. grep, wordcount, this jam between racks is not likely
> happen,
> > is it?
> >
> >
> > On Mon, Jun 6, 2011 at 11:40 PM, John Armstrong
> > <jo...@ccri.com>wrote:
> >
> >> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
> >> > Yeah, that's a good point.
> >> >
> >> > I wonder though, what the load on the tracker nodes (port et. al)
> would
> >> > be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
> >> >
> >> > Seems to me that if there is that much traffic being mitigate across
> >> > racks, that the tracker node (or whatever node it is) would overload
> >> > first?
> >>
> >> It could happen, but I don't think it would always. For example,
> tracker
> >> is on rack A; sees that the best place to put reducer R is on rack B;
> >> sees
> >> reducer still needs a few hellabytes from mapper M on rack C; tells M
> to
> >> send data to R; switches on B and C get throttled, leaving A free to
> >> handle
> >> other things.
> >>
> >> In fact, it almost makes me wonder if an ideal setup is not only to
> have
> >> each of the main control daemons on their own nodes, but to put THOSE
> >> nodes
> >> on their own rack and keep all the data elsewhere.
> >>
Re: Why inter-rack communication in mapreduce slow?
Posted by da...@ontrenet.com.
IMO, that's right. Because map/reduce/hadoop was originally designed for
that kind of text processing purpose. (i.e. few stages, low dependency,
highly parallel).
Its when one tries to solve general purpose algorithms of modest
complexity that map/reduce gets into I/O churning problems.
On Mon, 6 Jun 2011 23:58:53 +1000, elton sky <el...@gmail.com>
wrote:
> Hi John,
>
> Because for map task, job tracker tries to assign them to local data
nodes,
> so there' not much n/w traffic.
> Then the only potential issue will be, as you said, reducers, which
copies
> data from all maps.
> So in other words, if the application only creates small intermediate
> output, e.g. grep, wordcount, this jam between racks is not likely
happen,
> is it?
>
>
> On Mon, Jun 6, 2011 at 11:40 PM, John Armstrong
> <jo...@ccri.com>wrote:
>
>> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
>> > Yeah, that's a good point.
>> >
>> > I wonder though, what the load on the tracker nodes (port et. al)
would
>> > be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>> >
>> > Seems to me that if there is that much traffic being mitigate across
>> > racks, that the tracker node (or whatever node it is) would overload
>> > first?
>>
>> It could happen, but I don't think it would always. For example,
tracker
>> is on rack A; sees that the best place to put reducer R is on rack B;
>> sees
>> reducer still needs a few hellabytes from mapper M on rack C; tells M
to
>> send data to R; switches on B and C get throttled, leaving A free to
>> handle
>> other things.
>>
>> In fact, it almost makes me wonder if an ideal setup is not only to
have
>> each of the main control daemons on their own nodes, but to put THOSE
>> nodes
>> on their own rack and keep all the data elsewhere.
>>
Re: Why inter-rack communication in mapreduce slow?
Posted by elton sky <el...@gmail.com>.
Hi John,
Because for map task, job tracker tries to assign them to local data nodes,
so there' not much n/w traffic.
Then the only potential issue will be, as you said, reducers, which copies
data from all maps.
So in other words, if the application only creates small intermediate
output, e.g. grep, wordcount, this jam between racks is not likely happen,
is it?
On Mon, Jun 6, 2011 at 11:40 PM, John Armstrong <jo...@ccri.com>wrote:
> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
> > Yeah, that's a good point.
> >
> > I wonder though, what the load on the tracker nodes (port et. al) would
> > be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
> >
> > Seems to me that if there is that much traffic being mitigate across
> > racks, that the tracker node (or whatever node it is) would overload
> > first?
>
> It could happen, but I don't think it would always. For example, tracker
> is on rack A; sees that the best place to put reducer R is on rack B; sees
> reducer still needs a few hellabytes from mapper M on rack C; tells M to
> send data to R; switches on B and C get throttled, leaving A free to handle
> other things.
>
> In fact, it almost makes me wonder if an ideal setup is not only to have
> each of the main control daemons on their own nodes, but to put THOSE nodes
> on their own rack and keep all the data elsewhere.
>
Re: Why inter-rack communication in mapreduce slow?
Posted by James Seigel <ja...@tynt.com>.
Not sure that will make the interconnect faster, but it is worth a try.
On Mon, Jun 6, 2011 at 7:44 PM, Mauricio Cavallera <mc...@gmail.com> wrote:
> Unsubscribe
> El jun 6, 2011 10:54 a.m., "Joey Echeverria" <jo...@cloudera.com> escribió:
>> Most of the network bandwidth used during a MapReduce job should come
>> from the shuffle/sort phase. This part doesn't use HDFS. The
>> TaskTrackers running reduce tasks will pull intermediate results from
>> TaskTrackers running map tasks over HTTP. In most cases, it's
>> difficult to get rack locality during this process because of the
>> contract between mappers and reducers. If you wanted locality, your
>> data would already have to be grouped by key in your source files and
>> you'd need to use a custom partitioner.
>>
>> -Joey
>>
>> On Mon, Jun 6, 2011 at 9:49 AM, <da...@ontrenet.com> wrote:
>>>
>>> Yeah, the way you described it, maybe not. Because the hellabytes
>>> are all coming from one rack. But in reality, wouldn't this be
>>> more uniform because of how hadoop/hdfs work (distributed more evenly)?
>>>
>>> And if that is true, then for all the switched packets passing through
>>> the inter-rack switch, a consultation to the tracker would have preceeded
>>> it?
>>>
>>> Well, I'm just theorizing, and I'm sure we'll see more concrete numbers
>>> on the relation between # racks, # nodes, # switches, # trackers and
>>> their configurations.
>>>
>>> I like your idea about racking the trackers though. so it won't need any
>>> tracker trackers?!? ;)
>>>
>>> On Mon, 06 Jun 2011 09:40:12 -0400, John Armstrong
>>> <jo...@ccri.com> wrote:
>>>> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
>>>>> Yeah, that's a good point.
>>>>>
>>>>> I wonder though, what the load on the tracker nodes (port et. al) would
>>>>> be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>>>>>
>>>>> Seems to me that if there is that much traffic being mitigate across
>>>>> racks, that the tracker node (or whatever node it is) would overload
>>>>> first?
>>>>
>>>> It could happen, but I don't think it would always. For example,
>>> tracker
>>>> is on rack A; sees that the best place to put reducer R is on rack B;
>>> sees
>>>> reducer still needs a few hellabytes from mapper M on rack C; tells M to
>>>> send data to R; switches on B and C get throttled, leaving A free to
>>> handle
>>>> other things.
>>>>
>>>> In fact, it almost makes me wonder if an ideal setup is not only to have
>>>> each of the main control daemons on their own nodes, but to put THOSE
>>> nodes
>>>> on their own rack and keep all the data elsewhere.
>>>
>>
>>
>>
>> --
>> Joseph Echeverria
>> Cloudera, Inc.
>> 443.305.9434
>
Re: Why inter-rack communication in mapreduce slow?
Posted by Mauricio Cavallera <mc...@gmail.com>.
Unsubscribe
El jun 6, 2011 10:54 a.m., "Joey Echeverria" <jo...@cloudera.com> escribió:
> Most of the network bandwidth used during a MapReduce job should come
> from the shuffle/sort phase. This part doesn't use HDFS. The
> TaskTrackers running reduce tasks will pull intermediate results from
> TaskTrackers running map tasks over HTTP. In most cases, it's
> difficult to get rack locality during this process because of the
> contract between mappers and reducers. If you wanted locality, your
> data would already have to be grouped by key in your source files and
> you'd need to use a custom partitioner.
>
> -Joey
>
> On Mon, Jun 6, 2011 at 9:49 AM, <da...@ontrenet.com> wrote:
>>
>> Yeah, the way you described it, maybe not. Because the hellabytes
>> are all coming from one rack. But in reality, wouldn't this be
>> more uniform because of how hadoop/hdfs work (distributed more evenly)?
>>
>> And if that is true, then for all the switched packets passing through
>> the inter-rack switch, a consultation to the tracker would have preceeded
>> it?
>>
>> Well, I'm just theorizing, and I'm sure we'll see more concrete numbers
>> on the relation between # racks, # nodes, # switches, # trackers and
>> their configurations.
>>
>> I like your idea about racking the trackers though. so it won't need any
>> tracker trackers?!? ;)
>>
>> On Mon, 06 Jun 2011 09:40:12 -0400, John Armstrong
>> <jo...@ccri.com> wrote:
>>> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
>>>> Yeah, that's a good point.
>>>>
>>>> I wonder though, what the load on the tracker nodes (port et. al) would
>>>> be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>>>>
>>>> Seems to me that if there is that much traffic being mitigate across
>>>> racks, that the tracker node (or whatever node it is) would overload
>>>> first?
>>>
>>> It could happen, but I don't think it would always. For example,
>> tracker
>>> is on rack A; sees that the best place to put reducer R is on rack B;
>> sees
>>> reducer still needs a few hellabytes from mapper M on rack C; tells M to
>>> send data to R; switches on B and C get throttled, leaving A free to
>> handle
>>> other things.
>>>
>>> In fact, it almost makes me wonder if an ideal setup is not only to have
>>> each of the main control daemons on their own nodes, but to put THOSE
>> nodes
>>> on their own rack and keep all the data elsewhere.
>>
>
>
>
> --
> Joseph Echeverria
> Cloudera, Inc.
> 443.305.9434
Re: Why inter-rack communication in mapreduce slow?
Posted by Joey Echeverria <jo...@cloudera.com>.
Most of the network bandwidth used during a MapReduce job should come
from the shuffle/sort phase. This part doesn't use HDFS. The
TaskTrackers running reduce tasks will pull intermediate results from
TaskTrackers running map tasks over HTTP. In most cases, it's
difficult to get rack locality during this process because of the
contract between mappers and reducers. If you wanted locality, your
data would already have to be grouped by key in your source files and
you'd need to use a custom partitioner.
-Joey
On Mon, Jun 6, 2011 at 9:49 AM, <da...@ontrenet.com> wrote:
>
> Yeah, the way you described it, maybe not. Because the hellabytes
> are all coming from one rack. But in reality, wouldn't this be
> more uniform because of how hadoop/hdfs work (distributed more evenly)?
>
> And if that is true, then for all the switched packets passing through
> the inter-rack switch, a consultation to the tracker would have preceeded
> it?
>
> Well, I'm just theorizing, and I'm sure we'll see more concrete numbers
> on the relation between # racks, # nodes, # switches, # trackers and
> their configurations.
>
> I like your idea about racking the trackers though. so it won't need any
> tracker trackers?!? ;)
>
> On Mon, 06 Jun 2011 09:40:12 -0400, John Armstrong
> <jo...@ccri.com> wrote:
>> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
>>> Yeah, that's a good point.
>>>
>>> I wonder though, what the load on the tracker nodes (port et. al) would
>>> be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>>>
>>> Seems to me that if there is that much traffic being mitigate across
>>> racks, that the tracker node (or whatever node it is) would overload
>>> first?
>>
>> It could happen, but I don't think it would always. For example,
> tracker
>> is on rack A; sees that the best place to put reducer R is on rack B;
> sees
>> reducer still needs a few hellabytes from mapper M on rack C; tells M to
>> send data to R; switches on B and C get throttled, leaving A free to
> handle
>> other things.
>>
>> In fact, it almost makes me wonder if an ideal setup is not only to have
>> each of the main control daemons on their own nodes, but to put THOSE
> nodes
>> on their own rack and keep all the data elsewhere.
>
--
Joseph Echeverria
Cloudera, Inc.
443.305.9434
Re: Why inter-rack communication in mapreduce slow?
Posted by da...@ontrenet.com.
Yeah, the way you described it, maybe not. Because the hellabytes
are all coming from one rack. But in reality, wouldn't this be
more uniform because of how hadoop/hdfs work (distributed more evenly)?
And if that is true, then for all the switched packets passing through
the inter-rack switch, a consultation to the tracker would have preceeded
it?
Well, I'm just theorizing, and I'm sure we'll see more concrete numbers
on the relation between # racks, # nodes, # switches, # trackers and
their configurations.
I like your idea about racking the trackers though. so it won't need any
tracker trackers?!? ;)
On Mon, 06 Jun 2011 09:40:12 -0400, John Armstrong
<jo...@ccri.com> wrote:
> On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
>> Yeah, that's a good point.
>>
>> I wonder though, what the load on the tracker nodes (port et. al) would
>> be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>>
>> Seems to me that if there is that much traffic being mitigate across
>> racks, that the tracker node (or whatever node it is) would overload
>> first?
>
> It could happen, but I don't think it would always. For example,
tracker
> is on rack A; sees that the best place to put reducer R is on rack B;
sees
> reducer still needs a few hellabytes from mapper M on rack C; tells M to
> send data to R; switches on B and C get throttled, leaving A free to
handle
> other things.
>
> In fact, it almost makes me wonder if an ideal setup is not only to have
> each of the main control daemons on their own nodes, but to put THOSE
nodes
> on their own rack and keep all the data elsewhere.
RE: Why inter-rack communication in mapreduce slow?
Posted by Michael Segel <mi...@hotmail.com>.
We've looked at the network problem for the past two years.
10GBe is now a reality. Even a year ago prices were still at a premium.
Because you now have 10GBe and you have 2TB drives at a price sweet spot, you really need to sit down and think out your cluster design.
You need to look at things in terms of power usage, density, cost and vendor relationships...
There's really more to this problem.
If you're looking at a simple answer, if you run 1 GBe TOR switches, buy a reliable switch that not only has better uplinks but allows you to bond ports to create a fatter pipe.
Arista and BladeNetworks (Now part of IBM) are producing some interesting switches and the prices aren't too bad. (Plus they claim to play nice with Cisco switches...)
If you're looking to build out a very large cluster... you really need to take a holistic approach.
HTH
-Mike
> Date: Tue, 7 Jun 2011 10:47:25 +0100
> From: stevel@apache.org
> To: common-user@hadoop.apache.org
> Subject: Re: Why inter-rack communication in mapreduce slow?
>
> On 06/06/2011 02:40 PM, John Armstrong wrote:
> > On Mon, 06 Jun 2011 09:34:56 -0400,<da...@ontrenet.com> wrote:
> >> Yeah, that's a good point.
>
> >
> > In fact, it almost makes me wonder if an ideal setup is not only to have
> > each of the main control daemons on their own nodes, but to put THOSE nodes
> > on their own rack and keep all the data elsewhere.
>
> I'd give them 10Gbps connection to the main network fabric, as with any
> ingress/egress nodes whose aim in life is to get data into and out of
> the cluster. There's a lot to be said for fast nodes within the
> datacentre but not hosting datanodes, as that way their writes get
> scattered everywhere -which is what you need when loading data into HDFS.
>
> You don't need separate racks for this, just more complicated wiring.
>
> -steve
>
> (disclaimer, my network knowledge generally stops at Connection Refused
> and No Route to Host messages)
Re: Why inter-rack communication in mapreduce slow?
Posted by Steve Loughran <st...@apache.org>.
On 06/06/2011 02:40 PM, John Armstrong wrote:
> On Mon, 06 Jun 2011 09:34:56 -0400,<da...@ontrenet.com> wrote:
>> Yeah, that's a good point.
>
> In fact, it almost makes me wonder if an ideal setup is not only to have
> each of the main control daemons on their own nodes, but to put THOSE nodes
> on their own rack and keep all the data elsewhere.
I'd give them 10Gbps connection to the main network fabric, as with any
ingress/egress nodes whose aim in life is to get data into and out of
the cluster. There's a lot to be said for fast nodes within the
datacentre but not hosting datanodes, as that way their writes get
scattered everywhere -which is what you need when loading data into HDFS.
You don't need separate racks for this, just more complicated wiring.
-steve
(disclaimer, my network knowledge generally stops at Connection Refused
and No Route to Host messages)
Re: Why inter-rack communication in mapreduce slow?
Posted by John Armstrong <jo...@ccri.com>.
On Mon, 06 Jun 2011 09:34:56 -0400, <da...@ontrenet.com> wrote:
> Yeah, that's a good point.
>
> I wonder though, what the load on the tracker nodes (port et. al) would
> be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
>
> Seems to me that if there is that much traffic being mitigate across
> racks, that the tracker node (or whatever node it is) would overload
> first?
It could happen, but I don't think it would always. For example, tracker
is on rack A; sees that the best place to put reducer R is on rack B; sees
reducer still needs a few hellabytes from mapper M on rack C; tells M to
send data to R; switches on B and C get throttled, leaving A free to handle
other things.
In fact, it almost makes me wonder if an ideal setup is not only to have
each of the main control daemons on their own nodes, but to put THOSE nodes
on their own rack and keep all the data elsewhere.
Re: Why inter-rack communication in mapreduce slow?
Posted by da...@ontrenet.com.
Yeah, that's a good point.
I wonder though, what the load on the tracker nodes (port et. al) would
be if a inter-rack fiber switch at 10's of GBS' is getting maxed.
Seems to me that if there is that much traffic being mitigate across
racks, that the tracker node (or whatever node it is) would overload
first?
if I recall correctly, in order for a intra-rack node to be
selected, the tracker service has to be consulted, putting further
load on it...
On Mon, 06 Jun 2011 09:28:57 -0400, John Armstrong
<jo...@ccri.com> wrote:
> On Mon, 06 Jun 2011 09:26:11 -0400, <da...@ontrenet.com> wrote:
>> I'm not a hadoop jedi, but in that case, wouldn't one of the hadoop
>> "trackers" get bottlenecked to resolve those dependencies?
>>
>> Again, this exposes the oddity of hadoop IMO, it tries to NOT
>> be I/O bound, but seems its very I/O bound...
>
> I'm not a jedi either, but I think that the key is in the word "tries".
> Distributed computing is extremely I/O bound, and Hadoop tries to bring
> that down to just very.
Re: Why inter-rack communication in mapreduce slow?
Posted by John Armstrong <jo...@ccri.com>.
On Mon, 06 Jun 2011 09:26:11 -0400, <da...@ontrenet.com> wrote:
> I'm not a hadoop jedi, but in that case, wouldn't one of the hadoop
> "trackers" get bottlenecked to resolve those dependencies?
>
> Again, this exposes the oddity of hadoop IMO, it tries to NOT
> be I/O bound, but seems its very I/O bound...
I'm not a jedi either, but I think that the key is in the word "tries".
Distributed computing is extremely I/O bound, and Hadoop tries to bring
that down to just very.
Re: Why inter-rack communication in mapreduce slow?
Posted by da...@ontrenet.com.
I'm not a hadoop jedi, but in that case, wouldn't one of the hadoop
"trackers" get bottlenecked to resolve those dependencies?
Again, this exposes the oddity of hadoop IMO, it tries to NOT
be I/O bound, but seems its very I/O bound...
sorry. not trying to shift the thread topic.
On Mon, 06 Jun 2011 09:21:51 -0400, John Armstrong
<jo...@ccri.com> wrote:
> On Mon, 06 Jun 2011 09:18:45 -0400, <da...@ontrenet.com> wrote:
>> I never understood how hadoop can throttle an inter-rack fiber switch.
>> Its supposed to operate on the principle of move-the-code to the data
>> because of the I/O cost of moving the data, right?
>
> But what happens when a reducer on rack A gets most of its input from
> mappers on rack A, but needs a serious chunk of data from mappers on
racks,
> B, C, D...
Re: Why inter-rack communication in mapreduce slow?
Posted by John Armstrong <jo...@ccri.com>.
On Mon, 06 Jun 2011 09:18:45 -0400, <da...@ontrenet.com> wrote:
> I never understood how hadoop can throttle an inter-rack fiber switch.
> Its supposed to operate on the principle of move-the-code to the data
> because of the I/O cost of moving the data, right?
But what happens when a reducer on rack A gets most of its input from
mappers on rack A, but needs a serious chunk of data from mappers on racks,
B, C, D...
Re: Why inter-rack communication in mapreduce slow?
Posted by da...@ontrenet.com.
I never understood how hadoop can throttle an inter-rack fiber switch.
Its supposed to operate on the principle of move-the-code to the data
because of the I/O cost of moving the data, right?
On Mon, 6 Jun 2011 09:01:48 -0400, Joey Echeverria <jo...@cloudera.com>
wrote:
> Larger Hadoop installations are space dense, 20-40 nodes per rack.
> When you get to that density with multiple racks, it becomes expensive
> to buy a switch with enough capacity for all of the nodes in all of
> the racks. The typical solution is to install a switch per rack with
> uplinks to a core switch to route between the racks. In this
> arrangement, you'll be limited by the uplink bandwidth to the core
> switch for interrack communication. Typically these uplinks are 10-20
> Gbps (bidirectional).
>
> Assuming you have 32 nodes in a rack with 1 Gbps links, then 20 Gbps
> isn't enough bandwidth to push all of those ports at full tilt between
> racks. That's why Hadoop has the ability to take advantage of rack
> locality. It will try to schedule I/O local to a rack where it's less
> likely to block.
>
> -Joey
>
> On Mon, Jun 6, 2011 at 7:04 AM, elton sky <el...@gmail.com>
wrote:
>> Thanks for reply, Steve,
>>
>> I totally agree benchmark is a good idea. But the problem is I don't
have
>> switch to play with rather than a small cluster.
>> I am curious of this and post the question.
>> Can some experienced ppl can share their knowledge with us?
>>
>> Cheers
>>
>> On Mon, Jun 6, 2011 at 7:28 PM, Steve Loughran <st...@apache.org>
wrote:
>>
>>> On 06/06/11 08:22, elton sky wrote:
>>>
>>>> hello everyone,
>>>>
>>>> As I don't have experience with big scale cluster, I cannot figure
out
>>>> why
>>>> the inter-rack communication in a mapreduce job is "significantly"
>>>> slower
>>>> than intra-rack.
>>>> I saw cisco catalyst 4900 series switch can reach upto 320Gbps
>>>> forwarding
>>>> capacity. Connected with 48 nodes with 1Gbps ethernet each, it should
>>>> not
>>>> be
>>>> much contention at the switch, is it?
>>>>
>>>
>>> I don't know enough about these switches; I do hear stories about
>>> buffering
>>> and the like, and I also hear that a lot of switches don't always
>>> expect all
>>> the ports to light up simultaneously.
>>>
>>> Outside hadoop, try setting up some simple bandwidth tests to measure
>>> inter-rack bandwidth: have every node on one rack try and talk to one
on
>>> another at full rate.
>>>
>>> Set up every node talking to every other node at least once, to make
>>> sure
>>> there aren't odd problems between two nodes, which can happen if one
of
>>> the
>>> NICs is playing up.
>>>
>>> Once you are happy that the basic bandwidth between servers is OK,
then
>>> it's time to start worrying adding hadoop to the mix
>>>
>>> -steve
>>>
>>
Re: Why inter-rack communication in mapreduce slow?
Posted by Joey Echeverria <jo...@cloudera.com>.
Larger Hadoop installations are space dense, 20-40 nodes per rack.
When you get to that density with multiple racks, it becomes expensive
to buy a switch with enough capacity for all of the nodes in all of
the racks. The typical solution is to install a switch per rack with
uplinks to a core switch to route between the racks. In this
arrangement, you'll be limited by the uplink bandwidth to the core
switch for interrack communication. Typically these uplinks are 10-20
Gbps (bidirectional).
Assuming you have 32 nodes in a rack with 1 Gbps links, then 20 Gbps
isn't enough bandwidth to push all of those ports at full tilt between
racks. That's why Hadoop has the ability to take advantage of rack
locality. It will try to schedule I/O local to a rack where it's less
likely to block.
-Joey
On Mon, Jun 6, 2011 at 7:04 AM, elton sky <el...@gmail.com> wrote:
> Thanks for reply, Steve,
>
> I totally agree benchmark is a good idea. But the problem is I don't have
> switch to play with rather than a small cluster.
> I am curious of this and post the question.
> Can some experienced ppl can share their knowledge with us?
>
> Cheers
>
> On Mon, Jun 6, 2011 at 7:28 PM, Steve Loughran <st...@apache.org> wrote:
>
>> On 06/06/11 08:22, elton sky wrote:
>>
>>> hello everyone,
>>>
>>> As I don't have experience with big scale cluster, I cannot figure out why
>>> the inter-rack communication in a mapreduce job is "significantly" slower
>>> than intra-rack.
>>> I saw cisco catalyst 4900 series switch can reach upto 320Gbps forwarding
>>> capacity. Connected with 48 nodes with 1Gbps ethernet each, it should not
>>> be
>>> much contention at the switch, is it?
>>>
>>
>> I don't know enough about these switches; I do hear stories about buffering
>> and the like, and I also hear that a lot of switches don't always expect all
>> the ports to light up simultaneously.
>>
>> Outside hadoop, try setting up some simple bandwidth tests to measure
>> inter-rack bandwidth: have every node on one rack try and talk to one on
>> another at full rate.
>>
>> Set up every node talking to every other node at least once, to make sure
>> there aren't odd problems between two nodes, which can happen if one of the
>> NICs is playing up.
>>
>> Once you are happy that the basic bandwidth between servers is OK, then
>> it's time to start worrying adding hadoop to the mix
>>
>> -steve
>>
>
--
Joseph Echeverria
Cloudera, Inc.
443.305.9434
Re: Why inter-rack communication in mapreduce slow?
Posted by elton sky <el...@gmail.com>.
Thanks for reply, Steve,
I totally agree benchmark is a good idea. But the problem is I don't have
switch to play with rather than a small cluster.
I am curious of this and post the question.
Can some experienced ppl can share their knowledge with us?
Cheers
On Mon, Jun 6, 2011 at 7:28 PM, Steve Loughran <st...@apache.org> wrote:
> On 06/06/11 08:22, elton sky wrote:
>
>> hello everyone,
>>
>> As I don't have experience with big scale cluster, I cannot figure out why
>> the inter-rack communication in a mapreduce job is "significantly" slower
>> than intra-rack.
>> I saw cisco catalyst 4900 series switch can reach upto 320Gbps forwarding
>> capacity. Connected with 48 nodes with 1Gbps ethernet each, it should not
>> be
>> much contention at the switch, is it?
>>
>
> I don't know enough about these switches; I do hear stories about buffering
> and the like, and I also hear that a lot of switches don't always expect all
> the ports to light up simultaneously.
>
> Outside hadoop, try setting up some simple bandwidth tests to measure
> inter-rack bandwidth: have every node on one rack try and talk to one on
> another at full rate.
>
> Set up every node talking to every other node at least once, to make sure
> there aren't odd problems between two nodes, which can happen if one of the
> NICs is playing up.
>
> Once you are happy that the basic bandwidth between servers is OK, then
> it's time to start worrying adding hadoop to the mix
>
> -steve
>
Re: Why inter-rack communication in mapreduce slow?
Posted by Steve Loughran <st...@apache.org>.
On 06/06/11 08:22, elton sky wrote:
> hello everyone,
>
> As I don't have experience with big scale cluster, I cannot figure out why
> the inter-rack communication in a mapreduce job is "significantly" slower
> than intra-rack.
> I saw cisco catalyst 4900 series switch can reach upto 320Gbps forwarding
> capacity. Connected with 48 nodes with 1Gbps ethernet each, it should not be
> much contention at the switch, is it?
I don't know enough about these switches; I do hear stories about
buffering and the like, and I also hear that a lot of switches don't
always expect all the ports to light up simultaneously.
Outside hadoop, try setting up some simple bandwidth tests to measure
inter-rack bandwidth: have every node on one rack try and talk to one on
another at full rate.
Set up every node talking to every other node at least once, to make
sure there aren't odd problems between two nodes, which can happen if
one of the NICs is playing up.
Once you are happy that the basic bandwidth between servers is OK, then
it's time to start worrying adding hadoop to the mix
-steve