Mapping of single request to multiple fields, M-Bus read request

Hey,
I do have an question about M-Bus devices. There are several things
which are quite specific to this standard.

When there is an read out request device answers with all values it does
have. Given my current (limited) knowledge about M-Bus, there is no way
to get single field. I believe it makes some sense since it is an bus
system where frame overhead matters.

Currently we miss a developer guidelines which would provide durection
for most common scenarios. I think in all other places it is rather
simple cause request items usually map to single (primitive) value in
the field device or complex type (user defined type) at most. That's why
we didn't need any major writing about above.

To put more context. Each reading of meter contains 0..N fields. Each
field have several points:
- Reported value (an int/decimal/string etc).
- Medium (ie. Electricity, Water, Gas)
- Function (instant value, min/max/avg value)
- Tariff
- Storage number (ie. actual or past month)

This means that for field request which is just "<slave-id>" we get N
fields whereas each field has several associated values. I guess that
some of values can be shifted to response metadata.
I need an advice how to handle this 1..N situation. I don't think we
have it in any other place. What driver should do?

Should it answer with:
- one field and struct with primitives
- one filed and struct of structs with all information
- multiple fields whereas answer for caller specified field will
contains List<String> indicating recognized field names.

I will also mention that for Wireless M-Bus situation is even more
complicated cause same device can report different set of fields. For
example there is one kind of frame every 15 seconds and another one
every 60 seconds.

Kind regards,
Łukasz

AW: AW: Mapping of single request to multiple fields, M-Bus read request

Posted by Christofer Dutz <ch...@c-ware.de>.
Hi Lukasz,

From your answer I still think that we are talking about the same thing ... 

If a user is interested in a field of a given device he asks for that field:

Field1: device1/somefield

The Driver reads all fields from the device and receives.

Response: 
- device1/something: value
- device1/somethingelse: value
- device1/somefield: value
- device1/yetanotherfield: value

And then the driver returns:
- device1/somefield: value 

To the client and simply discards the others. 

Now he could ask for:
- Field1: device1/something
- Field2: device1/somefield

Then the driver would also request only the state of one device and return:
- device1/ something: value
- device1/somefield: value

But if he would ask for 
- Field1: device1/something
- Field2: device2/somefieldonanotherdevice

Then it would need to request the state of two devices and return only one field of each.

That's what I meant.

Chris


-----Ursprüngliche Nachricht-----
Von: Łukasz Dywicki <lu...@code-house.org> 
Gesendet: Montag, 22. März 2021 14:57
An: dev@plc4x.apache.org
Betreff: Re: AW: Mapping of single request to multiple fields, M-Bus read request

Hey Chris,
Issue is slightly different than you indicated in your answer. There is one request (1) but multiple fields (N) and there is no way to read out partial information from device. Also device response contains all necessary bits to describe answer (self descriptive frame).
This means that driver will have all the information to form reply composed from multiple fields. Passing part of logic from driver to interceptor/optimizer seems to create more troubles. In such case answer is processed in two places instead of one. This is problem I would like to avoid.
If we go with optimizer path then we have also situation it will must buffer answer and take care about expiry of values.
There is no other metadata than "read out" so discovery should rely on pretty much the same code as driver.

Best,
Łukasz


On 22.03.2021 14:22, Christofer Dutz wrote:
> HI Lukasz,
> 
> I think the org.apache.plc4x.java.spi.optimizer.BaseOptimizer is your friend here.
> We use this for example in the S7 driver to intercept requests and to split them up into multiple requests and to bring the results back together again. I think in your case you would simply go through all items and for each device addressed in that, create one request that reads all fields of a device. When the results come back you pick only the required bits of information from the response and return that to the client.
> 
> Perhaps the "Optimizer" isn't that good of a name ... perhaps we 
> should rename it to "RequestInteceptor" which would sort of cover also 
> your usecase. In general it was intended to be used by a proposed 
> "optimizer" component to rewrite requests to be executed in the most 
> efficient way (Auto re-writing reading of 8 boolean fields to a byte 
> read behind the scenes)
> 
> Hope that helps.
> 
> Chris
> 
> 
> -----Ursprüngliche Nachricht-----
> Von: Łukasz Dywicki <lu...@code-house.org>
> Gesendet: Montag, 22. März 2021 13:55
> An: dev@plc4x.apache.org
> Betreff: Mapping of single request to multiple fields, M-Bus read 
> request
> 
> Hey,
> I do have an question about M-Bus devices. There are several things which are quite specific to this standard.
> 
> When there is an read out request device answers with all values it does have. Given my current (limited) knowledge about M-Bus, there is no way to get single field. I believe it makes some sense since it is an bus system where frame overhead matters.
> 
> Currently we miss a developer guidelines which would provide durection for most common scenarios. I think in all other places it is rather simple cause request items usually map to single (primitive) value in the field device or complex type (user defined type) at most. That's why we didn't need any major writing about above.
> 
> To put more context. Each reading of meter contains 0..N fields. Each field have several points:
> - Reported value (an int/decimal/string etc).
> - Medium (ie. Electricity, Water, Gas)
> - Function (instant value, min/max/avg value)
> - Tariff
> - Storage number (ie. actual or past month)
> 
> This means that for field request which is just "<slave-id>" we get N fields whereas each field has several associated values. I guess that some of values can be shifted to response metadata.
> I need an advice how to handle this 1..N situation. I don't think we have it in any other place. What driver should do?
> 
> Should it answer with:
> - one field and struct with primitives
> - one filed and struct of structs with all information
> - multiple fields whereas answer for caller specified field will contains List<String> indicating recognized field names.
> 
> I will also mention that for Wireless M-Bus situation is even more complicated cause same device can report different set of fields. For example there is one kind of frame every 15 seconds and another one every 60 seconds.
> 
> Kind regards,
> Łukasz
> 

Re: AW: Mapping of single request to multiple fields, M-Bus read request

Posted by Łukasz Dywicki <lu...@code-house.org>.
Hey Chris,
Issue is slightly different than you indicated in your answer. There is
one request (1) but multiple fields (N) and there is no way to read out
partial information from device. Also device response contains all
necessary bits to describe answer (self descriptive frame).
This means that driver will have all the information to form reply
composed from multiple fields. Passing part of logic from driver to
interceptor/optimizer seems to create more troubles. In such case answer
is processed in two places instead of one. This is problem I would like
to avoid.
If we go with optimizer path then we have also situation it will must
buffer answer and take care about expiry of values.
There is no other metadata than "read out" so discovery should rely on
pretty much the same code as driver.

Best,
Łukasz


On 22.03.2021 14:22, Christofer Dutz wrote:
> HI Lukasz,
> 
> I think the org.apache.plc4x.java.spi.optimizer.BaseOptimizer is your friend here.
> We use this for example in the S7 driver to intercept requests and to split them up into multiple requests and to bring the results back together again. I think in your case you would simply go through all items and for each device addressed in that, create one request that reads all fields of a device. When the results come back you pick only the required bits of information from the response and return that to the client.
> 
> Perhaps the "Optimizer" isn't that good of a name ... perhaps we should rename it to "RequestInteceptor" which would sort of cover also your usecase. In general it was intended to be used by a proposed "optimizer" component to rewrite requests to be executed in the most efficient way (Auto re-writing reading of 8 boolean fields to a byte read behind the scenes)
> 
> Hope that helps.
> 
> Chris 
> 
> 
> -----Ursprüngliche Nachricht-----
> Von: Łukasz Dywicki <lu...@code-house.org> 
> Gesendet: Montag, 22. März 2021 13:55
> An: dev@plc4x.apache.org
> Betreff: Mapping of single request to multiple fields, M-Bus read request
> 
> Hey,
> I do have an question about M-Bus devices. There are several things which are quite specific to this standard.
> 
> When there is an read out request device answers with all values it does have. Given my current (limited) knowledge about M-Bus, there is no way to get single field. I believe it makes some sense since it is an bus system where frame overhead matters.
> 
> Currently we miss a developer guidelines which would provide durection for most common scenarios. I think in all other places it is rather simple cause request items usually map to single (primitive) value in the field device or complex type (user defined type) at most. That's why we didn't need any major writing about above.
> 
> To put more context. Each reading of meter contains 0..N fields. Each field have several points:
> - Reported value (an int/decimal/string etc).
> - Medium (ie. Electricity, Water, Gas)
> - Function (instant value, min/max/avg value)
> - Tariff
> - Storage number (ie. actual or past month)
> 
> This means that for field request which is just "<slave-id>" we get N fields whereas each field has several associated values. I guess that some of values can be shifted to response metadata.
> I need an advice how to handle this 1..N situation. I don't think we have it in any other place. What driver should do?
> 
> Should it answer with:
> - one field and struct with primitives
> - one filed and struct of structs with all information
> - multiple fields whereas answer for caller specified field will contains List<String> indicating recognized field names.
> 
> I will also mention that for Wireless M-Bus situation is even more complicated cause same device can report different set of fields. For example there is one kind of frame every 15 seconds and another one every 60 seconds.
> 
> Kind regards,
> Łukasz
> 

AW: Mapping of single request to multiple fields, M-Bus read request

Posted by Christofer Dutz <ch...@c-ware.de>.
HI Lukasz,

I think the org.apache.plc4x.java.spi.optimizer.BaseOptimizer is your friend here.
We use this for example in the S7 driver to intercept requests and to split them up into multiple requests and to bring the results back together again. I think in your case you would simply go through all items and for each device addressed in that, create one request that reads all fields of a device. When the results come back you pick only the required bits of information from the response and return that to the client.

Perhaps the "Optimizer" isn't that good of a name ... perhaps we should rename it to "RequestInteceptor" which would sort of cover also your usecase. In general it was intended to be used by a proposed "optimizer" component to rewrite requests to be executed in the most efficient way (Auto re-writing reading of 8 boolean fields to a byte read behind the scenes)

Hope that helps.

Chris 


-----Ursprüngliche Nachricht-----
Von: Łukasz Dywicki <lu...@code-house.org> 
Gesendet: Montag, 22. März 2021 13:55
An: dev@plc4x.apache.org
Betreff: Mapping of single request to multiple fields, M-Bus read request

Hey,
I do have an question about M-Bus devices. There are several things which are quite specific to this standard.

When there is an read out request device answers with all values it does have. Given my current (limited) knowledge about M-Bus, there is no way to get single field. I believe it makes some sense since it is an bus system where frame overhead matters.

Currently we miss a developer guidelines which would provide durection for most common scenarios. I think in all other places it is rather simple cause request items usually map to single (primitive) value in the field device or complex type (user defined type) at most. That's why we didn't need any major writing about above.

To put more context. Each reading of meter contains 0..N fields. Each field have several points:
- Reported value (an int/decimal/string etc).
- Medium (ie. Electricity, Water, Gas)
- Function (instant value, min/max/avg value)
- Tariff
- Storage number (ie. actual or past month)

This means that for field request which is just "<slave-id>" we get N fields whereas each field has several associated values. I guess that some of values can be shifted to response metadata.
I need an advice how to handle this 1..N situation. I don't think we have it in any other place. What driver should do?

Should it answer with:
- one field and struct with primitives
- one filed and struct of structs with all information
- multiple fields whereas answer for caller specified field will contains List<String> indicating recognized field names.

I will also mention that for Wireless M-Bus situation is even more complicated cause same device can report different set of fields. For example there is one kind of frame every 15 seconds and another one every 60 seconds.

Kind regards,
Łukasz