Posted to dev@plc4x.apache.org by Gunther Gruber <gu...@IDA-Analytics.de> on 2019/03/06 12:40:30 UTC
S7 read multiple variables
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
460 [main] INFO com.ida.moira.collector.plc4j.PLCCollectorOperatorTest - Synchronous request ...
487 [nioEventLoopGroup-2-1] WARN io.netty.channel.DefaultChannelPipeline - An exceptionCaught() event was fired, and it reached at the tail of the pipeline. It usually means the last handler in the pipeline did not handle the exception.
io.netty.handler.codec.DecoderException: java.lang.NullPointerException
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:98)
at org.apache.plc4x.java.s7.netty.S7Protocol.channelRead(S7Protocol.java:410)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:102)
at io.netty.handler.codec.MessageToMessageCodec.channelRead(MessageToMessageCodec.java:111)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.handler.codec.ByteToMessageDecoder.fireChannelRead(ByteToMessageDecoder.java:310)
at io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:284)
at io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.channel.ChannelInboundHandlerAdapter.channelRead(ChannelInboundHandlerAdapter.java:86)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1434)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:965)
at io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:163)
at io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:645)
at io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:580)
at io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:497)
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:459)
at io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:886)
at io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
at java.lang.Thread.run(Thread.java:748)
Caused by: java.lang.NullPointerException
at org.apache.plc4x.java.s7.netty.S7Protocol.decodeVarPayload(S7Protocol.java:608)
at org.apache.plc4x.java.s7.netty.S7Protocol.decodePayloads(S7Protocol.java:580)
at org.apache.plc4x.java.s7.netty.S7Protocol.decode(S7Protocol.java:456)
at org.apache.plc4x.java.s7.netty.S7Protocol$1.decode(S7Protocol.java:85)
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:88)
... 31 more
Re: S7 read multiple variables
Posted by Julian Feinauer <j....@pragmaticminds.de>.
Hi,
short update (we just had a discussion offline).
This should be the Bug which will be fixed with release 0.3.1 as there are many 1 byte requests (Bool and Byte).
So
tl; dr; for chris: stfu : )
Julian
Am 07.03.19, 16:26 schrieb "Christofer Dutz" <ch...@c-ware.de>:
Hi Gunther,
I was a little surprised about your finding as it seems all items have even byte-number types so the fill-byte problem shouldn't occur.
And the splitting of requests should also work quite well for S7 ... In one POC we even read 2600 items in one logical request, which was automatically split up into 30 requests and correctly merged back together.
How did you avoid the problem. I would assume you found a bug ... so we should fix it.
Chris
Am 07.03.19, 15:29 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
Hi,
with some small tweaks in my code i can read all the variables from a s7-1500 with the 0.3 version. I will switch to 0.3.1 after release.
Thx for this awesome library.
Below some proof :)
timestamp driveSetFreqInPercent currentDrivePercent currentSpeedInRpm
1551966078526
50
50.0
690.0
1551966079540
50
50.0
690.0
On 3/6/19 1:51 PM, Tim Mitsch wrote:
Hello Gunther
This bug is known and we fixed it already in development branch.
The problem is not the amount of variables rather than one-byte variables like BOOL,BYTE,USINT, ... - Simens uses a filling-byte when acquiring a single one-byte request
Right now we have the bugfix-release 0.3.1 as RC1 in vote, so you can try using a checkout development-branch from GitHub or just wait a few days until vote is finished and the version is available on MavenCentral.
Or you can use the staging-repository by integrating that in your pom and change plc4x-version to 0.3.1: https://repository.apache.org/content/repositories/orgapacheplc4x-1008
Best
Tim
Am 06.03.19, 13:40 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
Re: S7 read multiple variables
Posted by Gunther Gruber <gu...@IDA-Analytics.de>.
I resolved it by doing multiple request instead of one big request, and i skipped a few boolean variables.
%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE
%I40:UINT,%Q2.5:BOOL,%Q3:UINT
%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%I58:WORD
%F1:BYTE
skipped (%F1.0-%1.3)
%F28.0:BOOL
%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL
On 3/7/19 4:26 PM, Christofer Dutz wrote:
Hi Gunther,
I was a little surprised about your finding as it seems all items have even byte-number types so the fill-byte problem shouldn't occur.
And the splitting of requests should also work quite well for S7 ... In one POC we even read 2600 items in one logical request, which was automatically split up into 30 requests and correctly merged back together.
How did you avoid the problem. I would assume you found a bug ... so we should fix it.
Chris
Am 07.03.19, 15:29 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
Hi,
with some small tweaks in my code i can read all the variables from a s7-1500 with the 0.3 version. I will switch to 0.3.1 after release.
Thx for this awesome library.
Below some proof :)
timestamp driveSetFreqInPercent currentDrivePercent currentSpeedInRpm
1551966078526
50
50.0
690.0
1551966079540
50
50.0
690.0
On 3/6/19 1:51 PM, Tim Mitsch wrote:
Hello Gunther
This bug is known and we fixed it already in development branch.
The problem is not the amount of variables rather than one-byte variables like BOOL,BYTE,USINT, ... - Simens uses a filling-byte when acquiring a single one-byte request
Right now we have the bugfix-release 0.3.1 as RC1 in vote, so you can try using a checkout development-branch from GitHub or just wait a few days until vote is finished and the version is available on MavenCentral.
Or you can use the staging-repository by integrating that in your pom and change plc4x-version to 0.3.1: https://repository.apache.org/content/repositories/orgapacheplc4x-1008
Best
Tim
Am 06.03.19, 13:40 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
--
Gunther Gruber
Software Developer
[cid:part1.87523B61.F2715364@ida-analytics.de]
Intelligent Data Analytics GmbH & Co. KG
c/o TechQuartier
Platz der Einheit 2
60327 Frankfurt
Telefon: +49 6421/4805274
Telefax: +49 6421/4805275
E-Mail: gunther.gruber@ida-analytics.de
Internet: www.ida-analytics.de<http://www.ida-analytics.de/>
Unternehmenssitz: Frankfurt am Main | Handelsregister beim Amtsgericht: Frankfurt am Main, Registernummer: HRA 49357 | USt. ID-Nr.: DE310205810 | Finanzamt: Frankfurt am Main
Persönlich haftende Gesellschafterin: IDA Intelligent Data Analytics GmbH | Sitz: Frankfurt am Main | Handelsregister beim Amtsgericht: Frankfurt am Main | Handelsregister-Nummer: HRB 106805 | Geschäftsführer: Mohamed Ayadi, Nils Björn Krugmann, Matthias Leinweber, Marc Seidemann
If you are not the addressee, please inform us immediately that you have received this e-mail by mistake, and delete it. We thank you for your support.
Re: S7 read multiple variables
Posted by Christofer Dutz <ch...@c-ware.de>.
Hi Gunther,
I was a little surprised about your finding as it seems all items have even byte-number types so the fill-byte problem shouldn't occur.
And the splitting of requests should also work quite well for S7 ... In one POC we even read 2600 items in one logical request, which was automatically split up into 30 requests and correctly merged back together.
How did you avoid the problem. I would assume you found a bug ... so we should fix it.
Chris
Am 07.03.19, 15:29 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
Hi,
with some small tweaks in my code i can read all the variables from a s7-1500 with the 0.3 version. I will switch to 0.3.1 after release.
Thx for this awesome library.
Below some proof :)
timestamp driveSetFreqInPercent currentDrivePercent currentSpeedInRpm
1551966078526
50
50.0
690.0
1551966079540
50
50.0
690.0
On 3/6/19 1:51 PM, Tim Mitsch wrote:
Hello Gunther
This bug is known and we fixed it already in development branch.
The problem is not the amount of variables rather than one-byte variables like BOOL,BYTE,USINT, ... - Simens uses a filling-byte when acquiring a single one-byte request
Right now we have the bugfix-release 0.3.1 as RC1 in vote, so you can try using a checkout development-branch from GitHub or just wait a few days until vote is finished and the version is available on MavenCentral.
Or you can use the staging-repository by integrating that in your pom and change plc4x-version to 0.3.1: https://repository.apache.org/content/repositories/orgapacheplc4x-1008
Best
Tim
Am 06.03.19, 13:40 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
Re: S7 read multiple variables
Posted by Gunther Gruber <gu...@IDA-Analytics.de>.
Hi,
with some small tweaks in my code i can read all the variables from a s7-1500 with the 0.3 version. I will switch to 0.3.1 after release.
Thx for this awesome library.
Below some proof :)
timestamp driveSetFreqInPercent currentDrivePercent currentSpeedInRpm
1551966078526
50
50.0
690.0
1551966079540
50
50.0
690.0
On 3/6/19 1:51 PM, Tim Mitsch wrote:
Hello Gunther
This bug is known and we fixed it already in development branch.
The problem is not the amount of variables rather than one-byte variables like BOOL,BYTE,USINT, ... - Simens uses a filling-byte when acquiring a single one-byte request
Right now we have the bugfix-release 0.3.1 as RC1 in vote, so you can try using a checkout development-branch from GitHub or just wait a few days until vote is finished and the version is available on MavenCentral.
Or you can use the staging-repository by integrating that in your pom and change plc4x-version to 0.3.1: https://repository.apache.org/content/repositories/orgapacheplc4x-1008
Best
Tim
Am 06.03.19, 13:40 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
Re: S7 read multiple variables
Posted by Gunther Gruber <gu...@IDA-Analytics.de>.
thx
On 3/6/19 1:51 PM, Tim Mitsch wrote:
Hello Gunther
This bug is known and we fixed it already in development branch.
The problem is not the amount of variables rather than one-byte variables like BOOL,BYTE,USINT, ... - Simens uses a filling-byte when acquiring a single one-byte request
Right now we have the bugfix-release 0.3.1 as RC1 in vote, so you can try using a checkout development-branch from GitHub or just wait a few days until vote is finished and the version is available on MavenCentral.
Or you can use the staging-repository by integrating that in your pom and change plc4x-version to 0.3.1: https://repository.apache.org/content/repositories/orgapacheplc4x-1008
Best
Tim
Am 06.03.19, 13:40 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
460 [main] INFO com.ida.moira.collector.plc4j.PLCCollectorOperatorTest - Synchronous request ...
487 [nioEventLoopGroup-2-1] WARN io.netty.channel.DefaultChannelPipeline - An exceptionCaught() event was fired, and it reached at the tail of the pipeline. It usually means the last handler in the pipeline did not handle the exception.
io.netty.handler.codec.DecoderException: java.lang.NullPointerException
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:98)
at org.apache.plc4x.java.s7.netty.S7Protocol.channelRead(S7Protocol.java:410)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:102)
at io.netty.handler.codec.MessageToMessageCodec.channelRead(MessageToMessageCodec.java:111)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.handler.codec.ByteToMessageDecoder.fireChannelRead(ByteToMessageDecoder.java:310)
at io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:284)
at io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.channel.ChannelInboundHandlerAdapter.channelRead(ChannelInboundHandlerAdapter.java:86)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1434)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:965)
at io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:163)
at io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:645)
at io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:580)
at io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:497)
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:459)
at io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:886)
at io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
at java.lang.Thread.run(Thread.java:748)
Caused by: java.lang.NullPointerException
at org.apache.plc4x.java.s7.netty.S7Protocol.decodeVarPayload(S7Protocol.java:608)
at org.apache.plc4x.java.s7.netty.S7Protocol.decodePayloads(S7Protocol.java:580)
at org.apache.plc4x.java.s7.netty.S7Protocol.decode(S7Protocol.java:456)
at org.apache.plc4x.java.s7.netty.S7Protocol$1.decode(S7Protocol.java:85)
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:88)
... 31 more
--
Gunther Gruber
Software Developer
[cid:part1.9E6E9A69.561C286F@ida-analytics.de]
Intelligent Data Analytics GmbH & Co. KG
c/o TechQuartier
Platz der Einheit 2
60327 Frankfurt
Telefon: +49 6421/4805274
Telefax: +49 6421/4805275
E-Mail: gunther.gruber@ida-analytics.de
Internet: www.ida-analytics.de<http://www.ida-analytics.de/>
Unternehmenssitz: Frankfurt am Main | Handelsregister beim Amtsgericht: Frankfurt am Main, Registernummer: HRA 49357 | USt. ID-Nr.: DE310205810 | Finanzamt: Frankfurt am Main
Persönlich haftende Gesellschafterin: IDA Intelligent Data Analytics GmbH | Sitz: Frankfurt am Main | Handelsregister beim Amtsgericht: Frankfurt am Main | Handelsregister-Nummer: HRB 106805 | Geschäftsführer: Mohamed Ayadi, Nils Björn Krugmann, Matthias Leinweber, Marc Seidemann
If you are not the addressee, please inform us immediately that you have received this e-mail by mistake, and delete it. We thank you for your support.
Re: S7 read multiple variables
Posted by Tim Mitsch <t....@pragmaticindustries.de>.
Hello Gunther
This bug is known and we fixed it already in development branch.
The problem is not the amount of variables rather than one-byte variables like BOOL,BYTE,USINT, ... - Simens uses a filling-byte when acquiring a single one-byte request
Right now we have the bugfix-release 0.3.1 as RC1 in vote, so you can try using a checkout development-branch from GitHub or just wait a few days until vote is finished and the version is available on MavenCentral.
Or you can use the staging-repository by integrating that in your pom and change plc4x-version to 0.3.1: https://repository.apache.org/content/repositories/orgapacheplc4x-1008
Best
Tim
Am 06.03.19, 13:40 schrieb "Gunther Gruber" <gu...@IDA-Analytics.de>:
I try to read multiple variables synchronous from a S7-1500 and get a exception. I use the code from the hello world example. When i split up the variables into smaller units like 5-8 it works. any suggestion on this? Is there a limit to the number of variables?
Gunther
String vars = "%Q73:WORD,%Q75:WORD,%I73:WORD,%I75:WORD,%I74:WORD,%I77:WORD,%F81.1:BOOL,%Q82:REAL,%F86:INT,%F89:REAL,%I40:INT,%Q2.5:BOOL,%Q3:INT,%I66:WORD,%Q20:REAL,%I61:WORD,%Q25:WORD,%I58.0:BOOL,%F1:BYTE,%F1.0:BOOL,%F1.1:BOOL,%F1.2:BOOL,%F1.3:BOOL,%F28.0:BOOL,%I58:WORD,%F0.7:BOOL,%F0.6:BOOL,%F0.5:BOOL,%F0.4:BOOL,%F0.3:BOOL,%F0.2:BOOL,%F0.1:BOOL,%F0.0:BOOL,%F0:BYTE";
for (String item : splitVariables(vars)){
variables.add(item);
}
460 [main] INFO com.ida.moira.collector.plc4j.PLCCollectorOperatorTest - Synchronous request ...
487 [nioEventLoopGroup-2-1] WARN io.netty.channel.DefaultChannelPipeline - An exceptionCaught() event was fired, and it reached at the tail of the pipeline. It usually means the last handler in the pipeline did not handle the exception.
io.netty.handler.codec.DecoderException: java.lang.NullPointerException
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:98)
at org.apache.plc4x.java.s7.netty.S7Protocol.channelRead(S7Protocol.java:410)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:102)
at io.netty.handler.codec.MessageToMessageCodec.channelRead(MessageToMessageCodec.java:111)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.handler.codec.ByteToMessageDecoder.fireChannelRead(ByteToMessageDecoder.java:310)
at io.netty.handler.codec.ByteToMessageDecoder.channelRead(ByteToMessageDecoder.java:284)
at io.netty.handler.codec.ByteToMessageCodec.channelRead(ByteToMessageCodec.java:103)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.channel.ChannelInboundHandlerAdapter.channelRead(ChannelInboundHandlerAdapter.java:86)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.AbstractChannelHandlerContext.fireChannelRead(AbstractChannelHandlerContext.java:340)
at io.netty.channel.DefaultChannelPipeline$HeadContext.channelRead(DefaultChannelPipeline.java:1434)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:362)
at io.netty.channel.AbstractChannelHandlerContext.invokeChannelRead(AbstractChannelHandlerContext.java:348)
at io.netty.channel.DefaultChannelPipeline.fireChannelRead(DefaultChannelPipeline.java:965)
at io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:163)
at io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:645)
at io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:580)
at io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:497)
at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:459)
at io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:886)
at io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
at java.lang.Thread.run(Thread.java:748)
Caused by: java.lang.NullPointerException
at org.apache.plc4x.java.s7.netty.S7Protocol.decodeVarPayload(S7Protocol.java:608)
at org.apache.plc4x.java.s7.netty.S7Protocol.decodePayloads(S7Protocol.java:580)
at org.apache.plc4x.java.s7.netty.S7Protocol.decode(S7Protocol.java:456)
at org.apache.plc4x.java.s7.netty.S7Protocol$1.decode(S7Protocol.java:85)
at io.netty.handler.codec.MessageToMessageDecoder.channelRead(MessageToMessageDecoder.java:88)
... 31 more