[jira] [Created] (PLC4X-239) Read DTL (Date and Time)
Stefano Bossi created PLC4X-239:
-----------------------------------
Summary: Read DTL (Date and Time)
Key: PLC4X-239
URL: https://issues.apache.org/jira/browse/PLC4X-239
Project: Apache PLC4X
Issue Type: Bug
Components: Driver-S7
Affects Versions: 0.8.0
Reporter: Stefano Bossi
Attachments: Screenshot 2020-08-19 at 17.02.58.png, correctDateAndTimeRead_v0_6_0.pcapng, wrongDateAndTimeRead_v0_8_0.pcapng
Dear developers,
I have found a bug in trying to read a Date and Time field from a S7 1200 PLC, here are the informations to help you in fixing the code.
I am using the HelloPlc4x application for testing, with this command line:
{code:java}
"--connection-string 's7://192.168.1.192' --field-addresses '%DB1:264.0:DATE_AND_TIME'"{code}
The Data Block in the PLC is like in the uploaded jpeg.
When I reach the line of code for the synchronous read request the code never return.
Via Wire Shark I have captured the dialog and I found that in the Read Var request only 1 byte is requested instead of the expected 8.
I have tried with the version 0.6.0 and in that release of the library are requested 8 byte correctly (the parsing after receiving the data fail for somewhat reason but via wireshark I could see that the data in the response is the correct Date and Time value I have on the PLC)
I attach the pcap capture with the 0.8.0 version and for comparison the one with the 0.6.0
Hope that this could help to have a more robust library.
Regards,
Stefano Bossi
--