[I] [Feature Request]: Force Function Code 6 when writing modbus tag
parthgoel06 opened a new issue, #2102:
URL: https://github.com/apache/plc4x/issues/2102
### What would you like to happen?
Is there a way that I can force the use of ModbusPDUWriteSingleRegisterRequest (Function Code 6) instead of ModbusPDUWriteMultipleHoldingRegistersRequest (Function Code 16) when I write a ModbusTCP tag? My device only accepts function code 6 when writing.
### Programming Languages
- [x] plc4j
- [ ] plc4go
- [ ] plc4c
- [ ] plc4net
### Protocols
- [ ] AB-Ethernet
- [ ] ADS /AMS
- [ ] BACnet/IP
- [ ] CANopen
- [ ] DeltaV
- [ ] DF1
- [ ] EtherNet/IP
- [ ] Firmata
- [ ] KNXnet/IP
- [x] Modbus
- [ ] OPC-UA
- [ ] S7
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904280143
If it's not for the high conversion rate from INR to EUR or $ I would have definitely donated more.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906768529
Your bigger proposed option would require the user to actively select an option in the connection string. In general, the work I'm currently doing is a prerequisite for this to work. So in this case the user selects the "single-register-writes" option and then the opimizer will let single-register tag writes pass without modification, but if you write a tag that is larger than one register, it will behind the scenes rewrite the tag into a series of single-register tags execute them and then merge the results back together. This should work on all devices ... but it's a lot more work to implement. And I wouldn't be willing to do that part for less than 400€ (I seem to have to add real price tags in order to avoid situations like this)
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904317906
Thanks and sorry if you felt that way, it was not my intention. Also, as I mentioned before to you, I'll try to get the company that I work for to donate a larger amount if they agree to it.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906735468
Can't we do something like this, where we introduce a new option when passing the address at the time of write?
For example, holding-register:20:UINT:single-write or holding-register:20:DINT:multi-write.
Or we can just default 16-bit data types to single write, but the user can overwrite it if needed using the multi-write option.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904130742
@chrisdutz I just donated you a coffee. If possible, can you do this implementation? 😁
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904297748
Well ... just checked and yeah ... thanks for the open-collective donation ... didn't see that connection, ... I'll have a look if I can squeeze it in somehow. I do know that finances are not spread out fairly over the globe. It just felt as if me fixing things wasn't worth much.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2903985690
So I am sending only 1 16-bit register per write request, but it's still writing with function code 16 (multiple register write). It works for most cases, but some manufacturers do not allow function code 16 for single register write.
Yeah, it would be great to have a config option in the address at the time of writing, where we can choose single or multi write.
I am currently going through the library code, but I'll definitely consider donating also 😁.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2899998451
HI,
should be quite easy to implement, if you want to give it a shot, I'm happy to help you scratch your own itch.
If not, there should also be some people in the community willing to help you out with this.
If you want me to do it. I stopped fixing and implementing stuff for free, so feel free to leave a donation here: https://buymeacoffee.com/christoferu (Doesn't have to be a huge one), then I'll take care of it.
Chris
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906802005
Great, thanks a lot 😁. I'll build the library again and try it myself for my use case.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904054448
Yeah ... I mentioned, that I might have "simplified" the driver to only use the one type as I couldn't see a benefit of having both (According to the Spec both should be supported, but it seems especially with Modbus, everyone does as he pleases).
So I guess you'll have to update the driver, or have someone update it for you.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904242925
So ... I would assume that I need to spend 1-2 hours on this fix and you just donated 5$ for that ... admittedly I'm slightly speachless.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906755961
Okay, sure, no issues. But let me understand it a bit clearly about your proposed option. Are you saying that implementing this would break multi-register write logic and it won't work? Wouldn't that be an issue for other people?
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2900558581
I would like to give implementation a shot, but would this implementation be done in the PLC4X library, or can I handle something in my service itself?
I have figured as much ->
In `plc4j/drivers/modbus/src/main/java/org/apache/plc4x/java/modbus/base/protocol/ModbusProtocolLogic.java` in `getWriteRequestPdu` function, when the tag is an instance of `ModbusTagHoldingRegister`, it defaults to `ModbusPDUWriteMultipleHoldingRegistersRequest`, which is a write request of function code 16.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906792418
So ... my changes are committed and if you pull them you should be able to use the single register reads.
<img width="1201" alt="Image" src="https://github.com/user-attachments/assets/5e217789-f5c5-43b3-8c41-f8dd9a729b6e" />
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906834062
It's working now, thanks a lot again. I'm closing this thread now.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2900720324
Well one option would be to do it on your application and simply create one item per request. However am I not sure that I didn't "clean up" the driver code to simply use the multi element option.
The more sustainable way (that others having the same problem would profit from) would be to add a cinfig option to the plc4x modbus driver implementation and update the protocol logic.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906746013
Well ... the option I proposed, would be simple to implement as I don't have to translate tags into intermediate tags. If I want to support this feature for all types of requests, I have to start doing request rewriting ... that's not something I do in 1-2 hours ... I think it's more something like the new Modbus Optimizer, that I built and that would be something down the lande of a full day to implement.
So it's not only about the time till it's finished ... it's about financing the work to do it.
I am currently implementing my proposed option as this is a quick win, that would allow you to communicate with your device, but forgive me that this is already 20 times more work than I would be willing to invest for 5$.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906740075
Also, I am not in much hurry, so you can take as much time as you want. I am also willing to help with this implementation if you can guide me. I tried to go through the library code but could not link how the higher-level APIs link to the protocol code.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906769971
Well, thanks for your work, it's really appreciated and the solution that you have implemented currently works too. And surely I'll keep in mind the donation part for the future.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2904265506
I would have donated more, but I already donated a good amount on Open Collective to PLC4X contribution and started the donation, just because I wanted to support you guys.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906766943
Well ... If I implement it the way I proposed (Well I already have and I'm currently testing it) if you write a tag that fits into one register, then it will automatically use the single register write (which should work for your use-case) ... if you send anything bigger, it will switch to the multi-register writes and that will not work on your device.
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "chrisdutz (via GitHub)" <gi...@apache.org>.
chrisdutz commented on issue #2102:
URL: https://github.com/apache/plc4x/issues/2102#issuecomment-2906456116
So yesterday I spent about an hour on the issue.
It's easy to implement something that uses the only one register method, if the tag is only one register big anyway. However, if it should break down multi register tags, that weighs be tricky and take a lot longer to implement.
Would that be a compromise?
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org
Re: [I] [Feature Request]: Force Function Code 6 when writing modbus tag
Posted by "parthgoel06 (via GitHub)" <gi...@apache.org>.
parthgoel06 closed issue #2102: [Feature Request]: Force Function Code 6 when writing modbus tag
URL: https://github.com/apache/plc4x/issues/2102
--
This is an automated message from the Apache Git Service.
To respond to the message, please log on to GitHub and use the
URL above to go to the specific comment.
To unsubscribe, e-mail: issues-unsubscribe@plc4x.apache.org
For queries about this service, please contact Infrastructure at:
users@infra.apache.org